    Ground wire to Gas Meter/Line?
    I live in Pasadena, California. We are installing a 200 amp Electrical Panel between a friend and I, he has more knowledge of electrical wiring than I do but he told me that we were going to install two copper grounding rods six feet apart near the box and run a line to the water main and another line to connect to the gas line, I feel that combining gas and electricity doesn't go together.
    Can you ground a line to the gas meter/line?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Jan 23, 2009, 09:44 PM

    It's called equipotential bonding. The water and gas need to be bonded near the point of entry (forget the specs).

    This is to make sure that all metal fixtures are at a 0 volt potential with respect to each other.

    The ground rod is primarily for lightning protection.

    Now, you wouldn't want to get shocked when touching your sink and stove with different hands at the same time, would you?
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #3

    Jan 23, 2009, 10:49 PM

    250.104(B) of the NEC says that any metal piping system that is likely to become energized must be bonded, including gas pipes.


    Suppose a water line became energized. The arc that could could happen between it and a gas line could easily ignite the gas. To avoid an arc between them you need to make sure they are at the same potential as each other. To do that you bond them.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jan 24, 2009, 06:10 AM
    250.104(B) also says that the equipment grounding conductor run with the circuit conductors feeding a gas appliance "shall be permitted to serve as the bonding means".

    We NEVER run an external additional bond for gas piping.




    250.104
    (B) Other Metal Piping. Where installed in or attached to a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.

    .
    .

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Misuse of ground wire as neutral return wire in old house [ 5 Answers ]

Here a problem where the "obvious" solution scares me, need some advice on how to best proceed. My home (built 1920 with knob and tube type wiring) has been upgraded over the years by prior owners, but in many place still has active current in the old wires, in other places it is spliced into a...

Water meter and air in line [ 3 Answers ]

Sometimes my water is turned off in my neighborhood. When it is back on the pressure is very hig, would air in the line and too much pressure cause the meter to read higher than norman. Thanks

Using the ground or (bare) wire for the neutral wire [ 2 Answers ]

I have a problem with some wiring that I ran for an outside motion light. Although the hot leg and ground wires are fine, the neutral wire is defective ( it may have gotten knicked or something). Of course, now the wiring is covered up behind a wall that I do not want to tear into if it can be...

Can you use Metal Conduit as ground to convert 2 wire to 3 wire? [ 3 Answers ]

I need to convert an old cinder block house from 2 wire outlets to 3 wire by adding a ground to all outlets. Since the entire house is cinder block, all the circuits from the basement breaker box are in flexible metal conduit and metal outlet boxes... Is it possible to use the metal conduit...

320 amp meter socket line wire [ 10 Answers ]

I am installing a new service with two meter panels. One 320 amp meter socket and one 200 amp meter socket. The 320 amp is a 400 amp socket panel with a disconect (two 200 amp breakers). What size of line in from the transformer wire do I need? It's a typical 3 wire, single phase service. Does...


View more questions Search