    York Diamond 80 Ignitor works abd blower runs but does not heat up house
    Our basement unit York Diamond 80 runs and run with the ignitor working and the blower running but does not heat up the first floor. The unit in the attic heats the first floor fine. The exhaust vent seems to be extremely hot. Is it possible the motor that exhausts the cabon monoxide from the gas fumes is running tto fast? The heat coming out of the registers is only reading 76.5. It has been running for three hours straight. The temp in the house is 61 degrees - upstairs is 65. Outside is 22. HELP
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 17, 2009, 03:16 PM
    You are only getting a 15 degree TD across the heat exchanger and that is low on output. Check to make sure the furnace filter is clean. If the unit is burning there is not much else you can do but call for an ON Site Inspection of your unit to determine the problem.

    What was the temperature before you turned the furnace on?
    msw's Avatar
    msw Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 17, 2009, 06:55 PM
    It was 60 degrees. It got down to -2.5 degress here in the Washington suburbs last night but the furnace clearly could not keek upo. It probably ran for 6 hrs staright. Tonight it ran for three hours before shutting off for 5 minutes only to run again for 30 minutes. It warmedup to 23 degrees and is suppose to warm up. It seems like it can not keep up eben though the Diamond 80 unit in the attic which is much colder has no problems keeping up - it is smaller biut only heats the seond floor. The unit for the basement and 1st floor just seems to run all the time.

    Suggestions?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 17, 2009, 10:11 PM
    You need to call for On Site srevice to get it looked into. I can do nothing from here with yor description. It is a good possibility that the unit needs to have the gas pressure checked to see if it meets the imput rate for the burner.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

York Diamond 80 heat blower cycles 20 seconds [ 9 Answers ]

Hi, I have a 1996 York Diamond 80 furnace. Everything starts up OK (thermostat fine, flue fan kicks on fine, then pilot orange glow, then click, then gas burners fire up, then main blower fan starts). This all happens in about a minute or so, but then the main fan only runs for 22 seconds, then it...

York Stellar Gas furnace Blower comes on NO heat [ 2 Answers ]

I am at a loss, furnace has a auto ignition, has tried to restart unit, but pilot does not appear to be one, air blows out of the vents, but no heat. :confused:

Blower works on A/C but not on heat or fan only [ 1 Answers ]

I have a 1997ish intertherm A/C unit, when the Air is on the blower works fine, but when I switch to heat or fan only the blower will not work? I have bought a new blower relay & capacitors. I tested the sequencers for 240 & 24 volt, everything is reading good. I am at a loss, does anyone have...

Blower on and ignitor is glowing, but no gas heat [ 1 Answers ]

I have a residential Carrier model. When heat is turned on, the blower comes on and the ignitor begins to glow, but the gas heat never fires. The gas valve is definitely turned on, and our hot water heater and oven work fine with gas heat. After the ignitor glows, I can hear a hissing sound for...

Blower fan works in A/C but not heat [ 8 Answers ]

A couple of weeks ago my Lennox G20Q3E-75-1 was acting up. Gas valve was cycling when calling for heat and then once satisfied and the main burners went out the pilot light was staying lit. I thought it might be the flame sensor as far as the gas valve cycling and didn't want to tear into it so I...


View more questions Search