    Bryant Day & Night Plus 90 --Poor Flame
    The symptoms started a few months ago with the Flame roll out switch tripping and setting a code. Upon resetting switch, furnace seemed to work properly for a couple of days. Then gradually over several weeks, the rollout switch needed to be reset hourly. When the burner flame ignites, flame quality seems poor and flame does not appear to be completely entering into combustion chamber, thus combustion chamber does not heat up, resulting in no(little) warm air in ducts. Rollout switch seems to be doing its job as temperature is heating up in ignition area.

    Steps taken: Replaced filter, inducer motor works fine, cleaned exterior of combustion chamber, verified proper blower operation, cleaned burner orifices (4). I suspect that the gas valve is faulty in not letting enough gas in to "push" flame into combustion chamber. Possible incorrect line pressure, but other appliances work fine.

    Is the gas valve a likely cause or what have I missed?
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #2

    Jan 4, 2009, 11:24 AM

    That is not how it works. The valve doesn't "push" the flame into the exchanger as much as the inducer "pulls" it. If the incoming pressure dropped off you would most likely see one or two burners ignite and the unit would ultimately shut off on the flame sensor. If your roll-out keeps tripping and the flame is not being pulled into the heat exchanger then I would suspect either something with the inducer/flue or a cracked heat exchanger. Either way you need to shut off your furnace and call in a service tech to inspect it.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Jan 4, 2009, 12:58 PM
    I agree call for service since this unit should have been looked at by a professional when the problem first surfaced.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Jan 4, 2009, 01:31 PM
    What you describe sounds like a restricted secondary heat exchanger (polypropylene lining collapsed). Go to furnaceclaims.com, your unit may qualify for the detailed warranty benefits.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Jan 4, 2009, 01:41 PM
    Carrier and bryant have a string of those problems.
    boondocker2's Avatar
    boondocker2 Posts: 2, Reputation: 1
    New Member
     
    #6

    Jan 4, 2009, 09:00 PM

    Thanks you all for your input! It is indeed a restricted secondary heat exchanger. New furnace will fix it. 15 years old is probably not worth repairing.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #7

    Jan 5, 2009, 04:18 AM
    Did you check out the website? W A R R A N T Y!! Why would you think a freebie isn't worth it?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant vs. Day and Night AC/Furnace [ 3 Answers ]

I have gotten bids from several companies for a gas furnace and central air. The Bryant and Day and Night dealers are the cheapest, although none of this is cheap. What opinions do you have about these companies? Should I hold out for Trane, Lennox?

Bryant furnace flame won't stay lit after a few minutes [ 8 Answers ]

I have a Bryant Plus 80 model 395C that is 17 years old. I turned the furnace on this weekend and it starts up just fine. The draft blower starts, the igniter glows, the valve opens and it lights the burners. After it heats up the blower comes on as always. After about 3-5 minutes the burner goes...

Bryant Furnace won't start flame on my emergency generator [ 4 Answers ]

My newer Bryant plus 80 T gas furnace would not start the flame when it was connected to my emergency generator during an ice storm that caused the commercial power to go out. Is this a result of the poor power quality of the emergency generator which messed up the electronic circuits of the...

No flame [ 1 Answers ]

My pilot won't ignite, and I get 3 flashes from the indicator light, stating either my pressure switch is jammed or vent is blocked, how do I know which is the problem, and is this something I can repair or do I need a specialist? [email protected]


View more questions Search