Make sure to change or keep your air filter clean at all times on mobiles.
One thing else I should have mentioned is gas pressure.
Having low gas pressure going to the burner (s) can also cause a fan to short cycle since the furnace is not running at full BTUs. If you have access to a pressure tester the label on the furnace will tell you the correct pressure. Natural gas usually 3.5 Propane usually 11 in water column.
If you do not have access to a gas pressure tester you can do the heat rise method. Take a thermometer and read the return air temp. Do the same on the discharge air temp. usually on the furnace label it will tell you what the heat rise range should be.
There are so many different items that can cause the same problem that one is picked and the other forgotten during posting. LOL
Always becareful if you are messing with propane.