I have an Intertherm MGHA-070 that is taking a very long time to come up to temp due to the blower fan coming on for approx 3 min. and switching off for about 30 seconds and keeping this cycle continuously and causing the burner to run constantly. I found a post from a year ago where HVAC1000 states it is the fan switch needing replacement. This was easy to find on the wiring diagram so I will change it out tomorrow. In his answer HVAC1000 mentioned that installing a larger blower motor will help move more air eliminating issues with air restrictions. Will it also make the furnace more efficient by moving warm air into the home faster so the burner is on a shorter time? Would it make enough of a difference to make it worthwhile to buy the larger fan?