    Coleman Electric Furnace - Limit Switches ?
    I have a Coleman 3300L823 (23Kw /78,000 BTU) furnace with 4 elements stacked vertically (bottom-up 1, 2, 3, 4) in the heater box above the blower .

    Sequencers are working correctly. The elements are all in good shape. However, when the weather gets around 0 degrees F, the furnace has a hard time keeping up with the natural heat loss of the house as elements 2, 3 & 4 are being switched on & off by the bi-metal limit switches connected in series to each element. It is a boderline situation, as the elements will cycle in & out as the limit switches detect 'a little too much heat'.

    These 4 limit switches are designed, I believe, to prevent an overheating element or elements from overheating the furnace and potentially cause a fire.

    The limit switches are not adjustable. I have tried spacing the limit switches to give them more a little more latitude or tolerance to radiated heat, but to no avail as the radiance from the lower elements reaches the next level of elements & the limit switches then knocks off elements 2, 3 & 4, sometimes only leaving the lowest element working.

    Other than bypassing some of the limit switches (defeating their purpose, and somewhat risky), any ideas/thoughts to solve this annoying problem.

    Thanks in advance.

    André (cadesmarais)
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Dec 13, 2008, 11:44 AM

    You are right, the limit switches only come into play if the unit is running too hot. Make sure the filter is clean, registers and returns aren't blocked, air conditioning coil isn't clogged with dirt (if equipped so), and correct blower speed is selected.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Dec 13, 2008, 12:42 PM
    Move more air across the elements to for the heat out. IE increase the blower speed.

    If this is in a mobile home high static of the ducts can be a problem.
    cadesmarais's Avatar
    cadesmarais Posts: 11, Reputation: 2
    New Member
     
    #4

    Dec 13, 2008, 04:57 PM
    Gents,. a further question - on a forced air electric furnace, what is a reasonable temperature differential when heating between return & supply sides?

    Testing it with 3 of four elements on, I noted 70-74 deg F on the return and close to 130 deg F on the supply... ie: just after the air handler.

    Thanks (CADesmarais)
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Dec 13, 2008, 05:00 PM
    Temp rise should be posted on the unit in degrees.

    On a side note: I am glad I will not have to pay your electric bill.
    cadesmarais's Avatar
    cadesmarais Posts: 11, Reputation: 2
    New Member
     
    #6

    Dec 13, 2008, 06:13 PM
    Hi again HVAC1001. Seems I can't rate your response before 'spreading ratings around' (whatever that means!)

    - No indication of temp rise indications on the unit or in the manual. Must say this unit is from the mid-eighties, so a lot of what's expected today of manufaturers was not then.

    ... about electricity bills & rates. Pointe-Claire (Montréal), Québec is darn cold early this year, but the hydro rates are also low... CAN $0.054 /Kwh, which at today's exchange is about US$0.043 /Kwh. In any event tomorrow's forecast is for a milder 30-32 F (~ 0 C).

    Best regards,. André (CADesmarais)
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Dec 13, 2008, 07:20 PM
    50-60 degrees rise is a bit high in my opinion for electric. Drop one of the heaters out and take another reading.
    cadesmarais's Avatar
    cadesmarais Posts: 11, Reputation: 2
    New Member
     
    #8

    Dec 20, 2008, 09:19 AM

    Hi again.

    An update FYI.

    The air handler was definitely looking for more fresh air. After some testing (removing a filter), I added an adjustable 4"x12" register just after the filter /before the evaporator coil and this settled the return air temperature so that the limit switches do not cut off power. I had to wait for a few colder days to confirm the problem solved.

    The filter bypass register will allow some unfiltered air through, about 12%, but it will recycle and eventually get filtered.

    Not a perfect solution, but it works!

    Many thanks to KC13 and HVAC100 for your tips and helping push the troubleshooting through to solving the problem.

    Best regards,. André (CADesmarais)
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #9

    Dec 20, 2008, 09:36 AM

    Well, okay, but this sounds more like symptom treatment that problem solving.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #10

    Dec 20, 2008, 10:06 AM
    At least it will keep working without droping out.
    cadesmarais's Avatar
    cadesmarais Posts: 11, Reputation: 2
    New Member
     
    #11

    Dec 20, 2008, 10:29 AM

    Hi.

    I agree. Hey - but it works!

    As I see it, the root problem is the furnace design where furnace elements are too close together and limit switches pick-up radiated heat from other lower elements.

    Also, adding the high efficiency filter last year has only made a borderline situation worse.

    Replacing the furnace, adding/enlarging several air returns or putting in a blower that runs a higher cfm (than manufacturer specified) are other solutions, but more $$$ to spend and noisier air flow I don't want for now.

    This air handler unit has served me well (since installed in '86) except in these somewhat extreme temprature conditions.

    Bear in mind that the air flow system in this house was built ('61) for oil heat forced air, which was converted to a heat pump/electric furnace in the mid-eighties. In such conversions, the air returns are almost always a problem because of the lower differentials.

    Thanks again for your help.

    Best regards,

    ... André (CADesmarais)
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #12

    Dec 20, 2008, 11:10 AM
    Return air is always a problem period. The only systems that have a guarantee return air performance is the old gravity systems. The old men (dead now) new that it had to be huge for the system to work. LOL

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Coleman Evcon electric furnace [ 2 Answers ]

I have a Coleman Evcon electric furnace in a mobile home I rent. Recently a wire had burned off which caused it to produce no heat. After they sent a repair man to work on it I now seem to not have as much air force coming out of the registers. Also it takes 20 minutes to raise the temperature one...

Coleman electric furnace [ 1 Answers ]

I have a coleman electric mobile home furnace and air conditioning unit. If the fan motor is in the automatic position the fan cycles on and off with cooling on. If it is in the heating position the fan will not come on but will come on in manual. I installed a new thermostat but still done the...

Coleman electric furnace [ 2 Answers ]

My blower won't come on. Even if I push the trematsate way up. What is causing this. But if I push the summer button on furnace then blower comes on

Coleman Evcon electric furnace [ 1 Answers ]

How do I know or rather how can I check to see if the repairman cut off one of the heating elements and where are they located?

Coleman electric furnace [ 2 Answers ]

I have a Coleman electric furnace in a mobile home. The furnace element turns on and heats up with the thermostat turned down to 50 degrees and with the inside temperature at 68 degrees. The thermostat doesn't click for the blower to turn on until I turn it up past 70 degrees. Why is the element...


View more questions Search