    Bonding Natural Gas Piping
    I had a natural gas system installed in my home and bonding the pipe entering the home has been a problem with the inspector (VA - Fairfax County). Anyway my HVAC contractor grounded the black pipe to the cold water copper with #6 AWG; however, the inspector is telling us the pipe needs to be bonded all the way back to the main panel (opposite side of the house) with #6 AWG because the grounded copper could be replaced with CPVC at some point in the future and the ground lost... whatever. Anyway I looked in the VA Fuel Gas Code and NEC and they don't say that, just that th piping must be bonded to a grounding electrode. I asked about just ramming another ground rod in near the pipe or bonding it to a sub-panel I have near the piping on a #6 AWG feeder wire (60 amp panel). I'm just trying to prevent my contractor from having to run copper all the way around the house. Am I missing something or is this inspector just difficult?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Nov 24, 2008, 07:13 PM
    Where did you read that it must be "bonded" to an electrode?? This will do absolutely nothing.
    Bonding means mechanically and electrically connected together. It has NOTHING to do with the earth.

    If there is an electrical appliance connected to this gas piping then you pipe is already bonded.
    Tell your inspector to see NEC 250.104(B)

    (B) Other Metal Piping Where installed in or attached to
    a building or structure, metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.
    hlmccarter's Avatar
    hlmccarter Posts: 14, Reputation: 1
    New Member
     
    #3

    Nov 24, 2008, 07:15 PM
    Sorry I just mistyped when I said electrode! I'm not the electrician here :)... OK I read that part too. Ok I'm going to call them. Just wanted to make sure I had someone backup what I read.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Nov 24, 2008, 07:18 PM
    I have to ask. You are talking about hard gas piping, right? Not CSST. Or are you?
    hlmccarter's Avatar
    hlmccarter Posts: 14, Reputation: 1
    New Member
     
    #5

    Nov 24, 2008, 07:22 PM

    Nope hard black pipe. There is a CSST connection to the heater and to a grill out back, but that won't change anything right?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Nov 25, 2008, 04:56 AM
    No, not if it is not an electrical appliance.

    Now your area may have a specific requirement to externally bond the pipe. If your inspector demands this I would ask him exactly where it says this and how it reads. If it reads like the NEC there is NO requirement to bring it all the way back to the panel

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

ABS vs PVC piping [ 4 Answers ]

Nb this sight has advised me not to use capital letters. Due to re-shingling I have had to take down my solar panels for heating the swimming pool along with all of the 1 1/2" dia. Piping, which is pvc. As it is over 20 years old and has been subject to ultraviolet rays I intend to replace it...

Shower piping [ 5 Answers ]

I have a custom shower to plumb and the mixing valves and volume control valves are all 3/4" threaded fittings. I have 1/2" hot/cold supply coming in to feed the shower. I will be plumbing the shower for a shower head and hand held shower which are both 1/2" threaded fittings. My question is should...

PVC piping [ 6 Answers ]

Can you run Hot H2O in PVC pipe.I ran my water lines and I seem to have gotten something crossed in the kitchen.Dont know how but Have hot H2O coming from PVC and cold coming from CPVC? I can't get to where it ties in at because it is at the eave end of the house.:confused:

Pvc piping [ 3 Answers ]

Hi I am trying to fix my daughters beach wheelchair and it is made of pvc piping. One piece of the piping cracked. I brought the piece to Lowe's and they said it was structural grade pvc and they didn't carry it. It is color coded inside. Can anyone tell me what they know about this and where...

Piping [ 5 Answers ]

I would like to get the diagram and parts required for a deepwell water system with a pressurized tank. What do I need to get started?


View more questions Search