How do I change Luxaire furnace fan speed?
I have a Luxaire Model PCLU gas furnace. The fan runs on Hi speed when the Thermostat switch is set to "on". I would like the fan to run on Lo speed when the Thermostat is set to "on" and automatically switch to Hi speed in the cooling and heating cycles. What wiring do I have to change?
|
|
 |
Full Member
|
|
Nov 14, 2008, 02:57 PM
|
|
I've figured out a way to do it on a PBLU model and York heat pump with White-Rodgers controller. It was a little complicated but I figured out with some SPDT relays. The customer wanted the fan to run on low speed to stir the air when they burned wood, but wanted the system to override that and run on high if the HP or furnace were called by the tstat.
Your case may be much simpler. First, what is energized on your tstat when you call for heat (W) versus just the fan (G)? Next what fan outputs are energized on your controller when the G wire is energized versus W?
Finally, do you have A/C? You do not want the fan to run accidentally on this low speed or you will ice up your indoor coil
Posting pics would be helpful along with exact model of controller.
|
|
 |
New Member
|
|
Nov 15, 2008, 09:25 AM
|
|
Thanks DAC122
My son just bought this house. The controller is a White Rodgers Model 50A50-241.
I will measure what is energized on the tstat in the Heat, Cool & Fan modes. (he does have A/C)
I will also see what fan outputs are energized on the controller when the G wire is energized.
The Heat & Cool terminals on the controller are jumpered so that the Fan runs on Hi speed in both Heat & Cool cycles.
The Red & Blue wires (Lo & Medium speed) fan wires are on Park terminals.
There are also 2 other terminals called EAC & HUM.
|
|
 |
Full Member
|
|
Nov 15, 2008, 09:28 PM
|
|
With A/C let me know if the Y terminal is also wired up/energized.
FYI I believe with that controller if W is energized fan HEAT terminal is energized; G and/or Y is energized fan COOL terminal is energized. But your stat could be energizing W and G for heat and Y and G for cool. And yes, both COOL and HEAT are set to fan high speed (black wire) from the factory, with other speeds on PARK - which does nothing. HUM is to energize an 110VAC add-on humidifier and EAC for some type of air cleaner.
|
|
 |
Senior Member
|
|
Nov 16, 2008, 09:10 AM
|
|
A typical conventional split system will be factory wired with the LOW speed used for heat. Changing this speed is fine but you have to be certain that your temperature rise is within factory specs. One common misconception is that a higher blower speed will result in more heat. The reality is that the exact opposite can be true. Make sure your heat rise is within the specs listed on your furnace's name plate.
|
|
 |
Full Member
|
|
Nov 16, 2008, 08:26 PM
|
|
Since the OP does not want to change the factory speed from high during heat or cool I believe there is no risk with heat rise or frosting. OP just wants to lower fan speed when not in heat or cool mode.
|
|
 |
New Member
|
|
Nov 17, 2008, 05:35 PM
|
|
dac122
With the tstat in "fan on" position the Cool terminal is energized on the 50A51 controller. I removed the jumper between the Heat & Cool terminals leaving the black fan wire on the Heat terminal. I also placed the Red fan wire (low speed) o the Cool terminal. The fan runs on low speed until the tstat calls for heat, then it runs on high speed. I shut the A/C breakers off with a note to remove the red wire from the Cool terminal and to replace the jumper between the Heat & Cool terminals.
This controller needs a separate terminal that is energized when the G wire is energized - then I wouldn't have to switch wires for summer/winter operation.
Thanks dac122, your earlier comments got me on to the right line of thought!
|
|
 |
Senior Member
|
|
Nov 17, 2008, 06:09 PM
|
|
 Originally Posted by dac122
Since the OP does not want to change the factory speed from high during heat or cool I believe there is no risk with heat rise or frosting. OP just wants to lower fan speed when not in heat or cool mode.
 Originally Posted by dhei
I would like the fan to run on Lo speed when the Thermostat is set to "on" and automatically switch to Hi speed in the cooling and heating cycles.
He never mentioned if the blower is already wired for high speed on the heating cycle. If not then it would be a good idea to check the heat rise.
|
|
 |
New Member
|
|
Nov 17, 2008, 07:04 PM
|
|
Mark, I mentioned in my first response to dac that the Heat & Cool terminals are jumpered and that the fan runs on Hi speed
|
|
 |
Full Member
|
|
Nov 17, 2008, 08:23 PM
|
|
 Originally Posted by dhei
dac122
With the tstat in "fan on" position the Cool terminal is energized on the 50A51 controller. I removed the jumper between the Heat & Cool terminals leaving the black fan wire on the Heat terminal. I also placed the Red fan wire (low speed) o the Cool terminal. The fan runs on low speed until the tstat calls for heat, then it runs on high speed. I shut the A/C breakers off with a note to remove the red wire from the Cool terminal and to replace the jumper between the Heat & Cool terminals.
This controller needs a separate terminal that is energized when the G wire is energized - then I wouldn't have to switch wires for summer/winter operation.
Thanks dac122, your earlier comments got me on to the right line of thought!
That should work for you with the A/C breaker turned off. Unfortuantely, when I did it I had to wire it to a Heat Pump for all season use. So two Single Pull Double Throw (SPDT) relays acted as a type of inclusive OR-gate so that if either the W or Y terminals were energized (or both) the fan would be switched to high speed. Once it was wired in there was no more thinking about it.
I can send or dictate a diagram if interested.
|
|
 |
New Member
|
|
Nov 18, 2008, 06:35 AM
|
|
I would be interested in seeing your diagram or an explanation of how the SPDT relays are wired in.
|
|
 |
Full Member
|
|
Nov 18, 2008, 08:10 AM
|
|
 Originally Posted by dhei
I would be interested in seeing your diagram or an explanation of how the SPDT relays are wired in.
I'm working from memory here, but I believe this is what I did. I assume the relays float right when energized. Make sure you use the proper gauge wire and have proper sized relays. Hope this helps.
|
|
 |
New Member
|
|
Nov 29, 2008, 07:06 PM
|
|
 Originally Posted by dac122
That should work for you with the A/C breaker turned off. Unfortuantely, when I did it I had to wire it to a Heat Pump for all season use. So two Single Pull Double Throw (SPDT) relays acted as a type of inclusive OR-gate so that if either the W or Y terminals were energized (or both) the fan would be switched to high speed. Once it was wired in there was no more thinking about it.
I can send or dictate a diagram if interested.
I have the same problem to solve. What are the part numbers, brand and source of the spdt relays? Would you be able to send that diagram?
|
|
 |
Full Member
|
|
Nov 29, 2008, 08:30 PM
|
|
Try ordering from here. What part of the diagram are you having trouble seeing?
|
|
 |
Heating & Air Conditioning Expert
|
|
Nov 29, 2008, 08:43 PM
|
|
The ultimate fan control. Got to know the owner many years ago. I use these on all 3 air handlers in my personal residence and sold 100's of them to customers. Great product especially with electronic air cleaners.
http://www.fanhandler.com/spec%201.pdf
I must say the relays will work and it can be done cheap that way but this control setup is the ultimate.
|
|
 |
New Member
|
|
Nov 29, 2008, 08:44 PM
|
|
 Originally Posted by dac122
Try ordering from here. What part of the diagram are you having trouble seeing?
Thanks dac122. That is great.
|
|
 |
Full Member
|
|
Nov 30, 2008, 06:20 PM
|
|
 Originally Posted by hvac1000
The ultimate fan control. Got to know the owner many years ago. I use these on all 3 air handlers in my personal residence and sold 100's of them to customers. Great product especially with electronic air cleaners.
http://www.fanhandler.com/spec%201.pdf
I must say the relays will work and it can be done cheap that way but this control setup is the ultimate.
Looks very promising hvac1000.
No exactly clear on this but does it try to mimic a VS fan with many speeds; or does it just run the low or high exclusively; or does it somehow modulate the low and/or high speeds? Curious what's inside that Fan Relay Electronic Module.
Do they still sell it, and what is the price?
|
|
 |
Heating & Air Conditioning Expert
|
|
Nov 30, 2008, 06:24 PM
|
|
It modulates from slow to full and back depending upon temperature. It has full variable speed control. I would never buy a VS fan unit from the furnace companys. Replacement parts are way to hight in cost and the energy savings is not there. This unit is designed for complete comfort.
They are sold the HVAC professionals in the trade.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Changing furnace fan speed to change delta
[ 7 Answers ]
I have a 12 year old Goodman furnace. About 3 years ago, I asked a service tech if there was anything that can be done to get warmer air out of the registers. He said he slowed the blower speed to get a higher temperature rise.
I had the ductwork replaced and it is smaller than the original...
Luxaire Furnace
[ 1 Answers ]
Our furnace at our second home runs the fan but no heat comes out.
This does not happen all the time.
Can be a problem because we are not here all the time
Luxaire Furnace Blowing Cold Air
[ 1 Answers ]
I came home this evening to find my luxair furnace running, but only cold air coming out of the vents. The led light is flashing 4 times. I replaced the filter, turned the furnace off for an hour, but the problem persists.
The owners guide indicates the 4 flashes indicates that the auxiliary...
Luxaire furnace
[ 1 Answers ]
My furnace cuts in and out far too often and my furnace will cut in and blow nothing but cold air. The red trouble shooting light flashes 8 times meaning "lockout caused by loss of flame" Any ideas why either of these situations happen?:confused:
I have put in a new flame sensor as well as a...
View more questions
Search
|