    Nov 2, 2005, 11:40 AM
    Changing furnace fan speed to change delta
    I have a 12 year old Goodman furnace. About 3 years ago, I asked a service tech if there was anything that can be done to get warmer air out of the registers. He said he slowed the blower speed to get a higher temperature rise.

    I had the ductwork replaced and it is smaller than the original ductwork and now it (the ductwork) gets pretty warm. I'd like to return the blower to its original high speed but I'm a little confused.

    I guess my confusion is due to a discrepency between what's hooked to the board and what is on the schematic.

    I have a Goodman GMP series furnace. Here's the color wires from the motor and what they are connected to:
    White goes to the NEUTRAL
    Orange is hooked to HEAT
    Black is hooked to COOL
    Red is hooked to M1
    Yellow is hooked to M2

    This is what the schematic calls for:

    Wh to Neutral
    BK to COOL
    Red to HEAT
    (*)Blue to M1
    Nothing on M2

    There are no Blue wires from the motor but the asterisk leads to a footnote that says "The leads from the motor may be changed to the required speed. Med HI-YELLOW; Med LOW- Orange. Remember, I'm trying to return fan to high speed to reduce temperature rise. Thanks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 2, 2005, 12:38 PM
    Looks like Black is your high speed. It may already be used for your A/C if you have one.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Nov 2, 2005, 12:55 PM
    If you want to use high speed for both heating and cooling, I think you could jumper the black to both heat and cool. The blower is controlled by separate relays, and I don't think the power would feed back to anything as long the other relay is open. You could also try switching Med HI-YELLOW and Med LOW- Orange. Sounds like they provide different intermediate speeds with yellow being higher than orange. The M1 and M2 may just be convenient places to keep unused wires out of trouble. See if the schematic shows anything connected to them.

    This may just put the wires back in their original position.
    rdu jetblast's Avatar
    rdu jetblast Posts: 3, Reputation: 1
    New Member
     
    #4

    Nov 2, 2005, 04:09 PM
    So, let's see if I understand this. What ever is hooked to the HEAT terminal determines the speed of the blower?

    And if I put red to heat as called for in the schematic, I will see a change in fan speed?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Nov 2, 2005, 06:28 PM
    It may be more complicated than that. I forgot about red. It is possible M1 or M2 may also be activated. Does your furnace have more than one firing rate? The blower speed may vary with the firing rate. You may just have to try different combinations.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Nov 2, 2005, 09:52 PM
    You could also use an isolation relay between heet and cool speed. I always worry about a back feed when both heat and cool are connected together to use the same speed.
    rdu jetblast's Avatar
    rdu jetblast Posts: 3, Reputation: 1
    New Member
     
    #7

    Nov 3, 2005, 05:28 AM
    Quote Originally Posted by labman
    It may be more complicated than that. I forgot about red. It is possible M1 or M2 may also be activated. Does your furnace have more than one firing rate? The blower speed may vary with the firing rate. You may just have to try different combinations.
    No, it has only one firing rate. The blower in not variable speed. And, I believe M1 & M2 do function somehow because the furnace won't come one if they are disconnected. As if they are part of the safety circuit. It can't be too complicated.
    wuchma's Avatar
    wuchma Posts: 2, Reputation: 1
    New Member
     
    #8

    Jan 16, 2011, 02:53 PM
    M1 and M2 are unused speeds

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between true air speed and equivalent air speed [ 4 Answers ]

What is the difference between the two and when an aircraft is flying at altitude what is its actual speed

Delta Shower Water control [ 2 Answers ]

I just had a new shower installed. It uses Delta rotary control from cold to hot.. Leaving it on HOT does not give burning HOT water.. Is thare some kind of a lock that limits how much hot water is supplied to the shower? My other shower(old) gives burning hot water in the HOT position - this...

Changing Last Name [ 1 Answers ]

My partner and I are planning to get married within the next year. However, neither of us wish to keep our current last name. Is it possible to create a new last name at the time of marriage and if so where could I find more information? We are living in Indianapolis, IN. I am a citizen and my...

Ceiling fan: change capacitor for single speed [ 3 Answers ]

I have a Loyal Products made in Taiwan fan with melted 4 wire capacitor. The capacitor has blue wire in and red 4uF, white 4.5uF and yellow 5uF wires out. This is connected to a two layer switch by the red and yellow wire. The white capacitor wire connects to a red wire going into the motor. My...

Epsilon delta proofs [ 2 Answers ]

Could someone prove the following: Lim * * x^3=8 X->2


View more questions Search