Its getting cold in here
Hello, I have a Coleman/Evcon gas forced air furnace that I just turned on. The motor comes on and the ignitor cycles through but nothing happens. After it cycles three times it shuts down and the indicator has a steady one blink/one blink/ one/blink etc.etc. Now last year I had to remove and clean the flame sensor at least twice if not three times could the flame sensor be the cause or am I looking at some other problem. If I don't get some heat in here quick my wife is going to start burning my clothes for heat.
|
|
 |
Heating & Air Conditioning Expert
|
|
Oct 23, 2008, 04:37 PM
|
|
If the furnace lites but goes out right away it could be the flame sensor.
|
|
 |
Ultra Member
|
|
Oct 23, 2008, 05:52 PM
|
|
If you have no flame after the ignitor starts to glow, check to make sure the gas valve is on inside the furnace and the gas shut off is open outside the furnace. If all is open and in the on position it may be just as simple as a dirty burner or burner orifice keeping the gas from hitting the ignitor.
|
|
 |
New Member
|
|
Oct 23, 2008, 07:32 PM
|
|
Okay both valves are on (especially since I never shut them off for any reason) and I ran a small nail inside the small gas outlet leading to the electronic ignitor. I replaced the cover and set the thermostat to come on but again the ignitor comes on three times before shutting down. No flame nothing. Do I have a bad gas valve? That's the only thing I can think of.
|
|
 |
New Member
|
|
Oct 24, 2008, 01:36 PM
|
|
 Originally Posted by lostnspace
okay both valves are on (especially since i never shut them off for any reason) and i ran a small nail inside the small gas outlet leading to the electronic ignitor. I replaced the cover and set the thermostat to come on but again the ignitor comes on three times before shutting down. no flame nothing. Do I have a bad gas valve? Thats the only thing I can think of.
Bump
|
|
 |
Heating & Air Conditioning Expert
|
|
Oct 24, 2008, 01:41 PM
|
|
If 24 volts is being supplied to the gas valve when it is supposed to be activated and the valve does not open it is probably the valve.
|
|
 |
New Member
|
|
Oct 24, 2008, 08:13 PM
|
|
Okay how do I test the voltage in idiots terms?
|
|
 |
New Member
|
|
Oct 24, 2008, 10:21 PM
|
|
O'K I think my problems is similar to yours. See "furnace circuit board??". When this happened late last winter, was told there was probably a shortage in the circuit board. The technician tightened the romex plug on the inducer motor and heat came back on. AC worked fine all summer, heat came on last week but gone out again. Watching replies to my thread may help with your problem too.
|
|
 |
Heating & Air Conditioning Expert
|
|
Oct 24, 2008, 11:03 PM
|
|
Okay how do I test the voltage in idiots terms?
Attach meter to low voltage leeds that activate gas valve. Start up furnace and observe meter. If no voltage is indicated on meter when the gas valve should be on the circuit board feeding the gas valve is probably defective. If 24 volts is observed at the meter and the gas valve is not operating then the gas valve is bad.
Unless you have the necessary skill to safely perform these tests I would suggest you call for professional ON SITE service from your local HVAC company.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Cold and drafty from ceiling mounted cold air return
[ 1 Answers ]
I recently purchased a adobe style home built in 2000 with a Single Roof Mounted combined HVAC system in the Albuquerque New Mexico Area. Directly below the HVAC is the only cold air return duct work located in the ceiling of the Hallway on one end of the Home. A single Thermostat for the entire...
Cold Snowblower great, cold dies
[ 2 Answers ]
I have an old Tech engine snowblower and it starts great and everything , but recently it has started acting-up it lacks power and dies when warmed-up please help:confused:
Furnace blowing cold air.starts out warm, goes to cold.
[ 6 Answers ]
Hoping for help here. I recently had my ignitor replaced. Before that, the furnace wasn't working at all. Now it starts blowing warm (not hot) air, then gradually over a period of a couple of hours, the air cools down until it is completely cold and the temperature in the house drops drastically....
Cold Air Registers Blowing Cold Air
[ 3 Answers ]
Our cold air registers are blowing cold air worse than if the windows were open. The hot air registers blow cold air but not as forceful (maybe because they are 1/3 the size of the returns) This only happens when the furnace is off and we are heating with the wood stoves. We have metal ducting...
View more questions
Search
|