    Adding a bus to a main panel for ground.
    I have recently added on a room to my house. I have a main power supply out side with a two pole 100 amp breaker the neutral and ground are on same bus, the ground continues down tocopper pole in ground. Upstream ihave added alager box to accommodate more poles. The new box has the two hot wires coming into a 200 amp breaker and the neutral to its desidnated area. There are two ground busses one on each side of the poles connected together by a copper plate. My question, do I need to add a separate bus for the ground and place all the bare wires to that bus and the white or neutral to the two buses? There is not one now but looks like there is a place for one to be added. Also, what is a NTL tie strap and when do you bond it or not bond it? This is a siemans box.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Oct 15, 2008, 10:04 AM
    Do you understand what you are doing? You do not add phase bus bars to a panel to increase its amperage. You can add additional ground and neutral busses providing your panel will accept them. You add them if there are not enough wholes available for ground or neutral conductors that are connected to your phase conductors that are mounted on the circuit breakers.

    You are describing a two phase 100 amp main panel. You should have two hot phases and a neutral. Each phase is protected by a 100 amp breaker.

    Since this is a main panel, Ground and Neutral are bonded at the main panel. Are you planning for the sub panel to be in the same building?

    Upstream you are describing a 200 amp sub panel, however, by virtue of the Service Supply limitation the most that panel can have supplied to it is 100 amps. If you have an independent service drop or lateral connection to a 200 amp supply, which is extremley unlikely since you can only have one source of service entry, and therefore you would have to feed the subpanel from the main.

    Exactly how are you doing that? Did you plan and install this subpanel by yourself? Has it been inspected by your LAHJ?

    Did you call an electrician to do this work for you? If not, I strongly suggest you get a licensed electrician review the installation with you.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Oct 15, 2008, 11:54 AM

    The NTS is basically described here:

    http://www2.sea.siemens.com/NR/rdonl...CU_4094705.pdf

    Ground needs to be run to the sub-panel and neutrals and grounds must remain separate in the panel. The removal of the NTS is that separation. Note that using main panels as sub-panels requires extra parts and removal of the Neutral Ground Strap.
    Usually you also have to purchase ground lug kit as well.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ground/Neutral Bus in Main Service Panel - Is there a Difference? [ 8 Answers ]

I'm preparing to provide new wiring to a sizable addition to a log home. Prior to beginning the new work I mapped my existing circuits thinking it best to correct any potential overloads in the existing panel/circuit design before introducing any new problems on my own. Decided to make a few...

Adding sub-panel to Main Panel [ 3 Answers ]

I am currently considering adding an ELECTRIC TANKLESS WATER HEATER. I have a 200 amp (ITE Load Panel G4040ML1200) with 37 of the 40 poles in use. The tankless water heater requires 4- 30amp breakers. My question is... how can I connect a 125 amp sub-panel to the main panel? Your comments are...

Adding a nuetral bus to an old main panel [ 5 Answers ]

Greetings... Can I add a neutral bus to my houses main panel... I have one bus in there now that is for both nuetral and ground... when I go to hookup the neutral from my 220 gfci breaker to that bus I keep tripping the breaker... the spa is a 3 wire 2 hots and a ground... the instructions say to...

Breaker size in main panel to support sub panel? [ 7 Answers ]

Hello, I am wiring a sub-panel to the outside of my home (50 feet from main 200 amp box). I ran 3 wire - 6 gauge. What is the largest 2 pole breaker I can put in the main panel to supply the sub-panel. TYPE NM-B 6-3 WITH GROUND 600 VOLTS CIRTEX-I EZ-STRIP (R) PLUS 17:11 2/5/07 SB/RC ...

Adding main electric panel in multi-family house [ 1 Answers ]

Hello, I just but a two-family (two levels) house in Gibbstown, NJ. The house only has one main circuit breaker panel feeding both apartments. My plan is to live in one unit and rent the other unit. Currently the house only has one electric power meter and one circuit breaker box. The meter...