    Blower not working with heater
    I had my blower quit on me about 1-2 months ago and I put a new blower motor in. I also put a new relay in at the same time.. now that I need the heat the blower does not come on..
    I can switch the switch from auto to on and it comes on, if I put it on AC it comes on also. When I flip it to heat, it ignites and the burners come on, also the exhaust fan/blower comes on but the main blower won't?
    Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 6, 2008, 02:36 PM
    There is a device that controls the blower in the heat mode. Usually called a fan and limit control on older furnaces. What is the make and exact model number of your furnace?
    rwcrazy's Avatar
    rwcrazy Posts: 7, Reputation: 1
    New Member
     
    #3

    Oct 6, 2008, 04:14 PM
    MODEL: PBNU-LD10N060D
    Computer(?): White Rodgers Div Emerson Electric
    I believe

    Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Oct 6, 2008, 04:41 PM
    Not the model of the circuit board but the brand and model of the furnace.

    White Rodgers Div Emerson Electric


    Sounds like it could be a Coleman or York furnace. Is this in a mobile home?
    White rodgers does not make furnaces they only make parts
    rwcrazy's Avatar
    rwcrazy Posts: 7, Reputation: 1
    New Member
     
    #5

    Oct 6, 2008, 05:07 PM
    Not a mobile home, there is no name just the model number, it is tan..
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Oct 6, 2008, 06:21 PM
    The furnace is tan? There is a plate on the inside of the wall near the burner.
    rwcrazy's Avatar
    rwcrazy Posts: 7, Reputation: 1
    New Member
     
    #7

    Oct 6, 2008, 06:36 PM
    There are 2 labels on the left side of the burners and they have the same thing on them,
    Model number pbnu-ld10n060d ser# ekam370482, on the bottom of that label it says central environmental systems
    Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Oct 6, 2008, 07:15 PM
    That has to be a York,Coleman,Luxair,Moncrief sister units. In other words they are made by York and labeled for there other companys/brands.

    Start by looking over the work you did before especially the relay wiring.

    There should be a combination fan limit control mounted in the front of the unit above the burners on the front wall.


    This unit should be a

    UPFLOW PROPANE GAS FURNACE 90+ with 3 burners

    Fan limit control part number L4064W1080

    Honeywell site for info

    Product

    Hope this helps
    rwcrazy's Avatar
    rwcrazy Posts: 7, Reputation: 1
    New Member
     
    #9

    Oct 6, 2008, 07:44 PM
    Is called the limit control?
    If so mine looks a lot different.
    This is what happened
    I purchased this home and put a new furance in about 15 yrs ago, about 1-2 months ago the blower stopped working, I went to grangers and picked up a replacement install that, some of the wires were different colors, but I thought I figured out what colors go where, the AC worked fine and the blower works fine if I with it from auto to on, its just in the heat mode it does not come on?
    Thanks a bunch
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #10

    Oct 6, 2008, 08:53 PM
    Yes it is called a fan and limit and they could have changed designs/ manufactures during manufacturing. The info I posted was right off a York corporation DVD I have . Well there is usually a different speed selected for the heat mode. Did you wire it up for both heat and cool when you replaced the motor?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #11

    Oct 6, 2008, 09:04 PM
    Until you get it figured out, there is no harm in letting the fan run continuously... just leave the fan switch in the on position. In fact many people do this to keep circulation in the home. When you switched your blower, was it during the cooling season?
    rwcrazy's Avatar
    rwcrazy Posts: 7, Reputation: 1
    New Member
     
    #12

    Oct 6, 2008, 09:06 PM
    Hmm not sure, I put the 2 browns on the relay, I put the black, (high speed) on grond power and I think that's it
    Going to bed, ill check this out in the morning

    Thanks a bunch
    rwcrazy's Avatar
    rwcrazy Posts: 7, Reputation: 1
    New Member
     
    #13

    Oct 7, 2008, 06:55 AM
    Not that I know of.. I just connected the high speed for the blower, do I need to connect another one for the heat to the same as the high speed?
    The old blower's wires were totally different than the new one?
    Thanks a bunch
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #14

    Oct 7, 2008, 09:59 AM
    Well you can connect to the same for high speed as long as the system will function wired like that but usually the blower runs slower for the heat mode but that is not absolutely necessary.

    The most important thing is that the blower motor is not supplied with two sources of power at the same time. IE high speed power applied and medium speed power applied at the same time. If that happens the motor will burn up.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heater blower noises [ 1 Answers ]

Hi my girlfreind lives in a mobile home,with original heat and air. I believe its around 1985. She describes a noises coming from blower but stops if you hit. I don't know if it does it any more after that. I think it comes and goes so she keeps hitting it.anybody have some ideas. Any ideas would...

Heat and Air not working on Attic unit, but blower working. [ 1 Answers ]

The blower is working fine on our Heating and Air Conditioning unit but neither the Air or Heat will work. The emergency Heat works fine though. The unit is a Carrier with the words American Standard written on the outside fan unit. What should I look for before calling a tech or what would this be...

Blower not working [ 2 Answers ]

Blower/fan will not turn on, replaced the transformer, but not the answer any ideas

Heater blower motor [ 4 Answers ]

Blower kicks on for a short time and then kicks off. It cycles repeatly, is it possibly hysterisis of the thermostat setting or furnace related? The model of our unit is: Intertherm Model 911030. It operates normally when there is a large differential between the temperature and thermostat...

Blower not working [ 3 Answers ]

I've got a Rheem Furnace which has the blower in it. The blower is also hooked up to a Trane AC unit. The blower does not come on but I hear a buzzing noise coming from either the transformer, or relay. I figured it was either the relay or capacitor and replaced them both for about $25. The motor...