    Thermostat issues outdoor boiler
    I've installed and am running a Central Boiler outdoor wood boiler heating two buildings. I have two propane forced air furnaces as backup. My furnace guy installed two 2stage heat/ 1-cool honeywell FocusPro5000. Problem-There is not enough tempreture difference between first and second stage heat. If there's a 2degree difference between stat setpoint and room temp, both stages come on. I emailed honeywell and was told all factors that determined when second stage kicked in, and that the 2-3 degree temp difference could not be changed. I want a 2stage heat/ 1 cool stat that I can have more control of. A 5-10 degree temp difference would be nice. I have heard of other outdoor boiler users using two stats to control. One stat controlling the fan only(outdoor boiler) and the second(forced air propane) as back-up- at a much lower setting. Any advice?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Oct 1, 2008, 09:21 AM
    Response wasn't appropriate.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Oct 1, 2008, 09:04 PM
    Most thermostats have pre-set stage differentials (or very limited ). Two thermostats may be the ticket to give you the differential you need. You are on the right track, redundant thermostats will give you what you want. I would appreciate a follow up on your progress since I am in the process of integrating a solar system for my domestic heat.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Oct 2, 2008, 04:24 AM
    Get two stage thermostats that allow a much larger differential is the easiest way to go since the wiring is already do for this type of set up.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #5

    Oct 6, 2008, 08:55 PM
    HVAC1000... like which thermostat? It's clear that it's what will work but what thermostats are available that have that great a differential? Manufacturer and model numbers please...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Oct 6, 2008, 09:32 PM
    Read

    Second Stage Time Delay
    Your thermostat is designed to determine the optimum time
    to activate the second stage. Simply raising the temperature
    in heating or lowering it in cooling will not always force the
    thermostat to bring the second stage on quickly. If the fast
    second stage option in the configuration menu (step 12) is
    set to "OFF", there is a delay from 0-30 minutes depending
    on the performance of the first stage of the system.
    EXAMPLE: For the last 2 hours the thermostat is set on 70°
    and the room temperature is 70° with the equipment using
    only the first stage of heat. Since the equipment is keeping
    the temperature within 1 degree of setpoint, the thermostat
    will delay second stage for a longer time if you manually
    raise the temperature or if the room temperature quickly
    changes. Once the second stage comes on, it will come on
    sooner the next time there is a difference between the
    setpoint and the room temperature. The net effect of the
    staging program is that when the first stage is capable of
    holding temperature, the second stage will delay longer.
    When the thermostat calculates that first stage cannot make
    temperature in a reasonable time, the second stage will
    come on sooner. This built in function automatically optimizes
    the use of additional stages of heat or cool.

    Unit

    http://www.white-rodgers.com/wrdhom/.../0037-6841.pdf


    There are others out there with similar features but I like this one since it is automatic.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Why does the boiler go on when thermostat is off ? [ 5 Answers ]

I just moved into a new house, and I don't think my boiler is working properly. I have a v8 oil boiler, when I turn off the thermostat it still keeps running. It turns on randomly for 5-10 minutes and then shut off and does this about 20 times a day. I changed the thermostat thinking that would...

Outdoor thermostat [ 1 Answers ]

How do you wire an outdoor thermostat on a rheem split system heat pump

Outdoor Plug Issues [ 5 Answers ]

Hi All! This is an awesome site! Today I noticed that my outdoor plug sockets are not working. There are two outdoor plug sets.. one in the front porch... and one in the backyard porch area. Anyway... the plug had a few Christmas light decorations plugged into it. Was working fine the...

Almost an Emergency (Boiler Issues) [ 1 Answers ]

Hi... I had 2 separate thermostats for my 2 fam house on 1 boiler. We disconnected the 2nd flr thermostat so it can all be run by the 1st floor thermostat. Of course like everything in this old house, the heat is not going on at all upstairs. Only on the 1st flr. Please help I need to...

Boiler issues [ 2 Answers ]

I have a water boiler with an external pump and an internal transformer as my heating source, controlled by a Honeywell programmable thermostat. The PROBLEM: #1. When I turn on my heat, the PUMP will NOT START sometimes! At times, it WILL START and run! Sometimes it will start but cycle off after...


View more questions Search