New Member
|
|
Sep 2, 2008, 03:29 PM
|
|
Possible bad transformer?
I wanted to get a second opinion if the transformer on my ac is dead. I've been all over the net looking up info, and I think I got it figured out. Here's an overview of what was wrong and what I've done:
Two units, one upstairs one down. Downstairs stopped working. No display on digital thermostat.
No 24v at thermostat. Swapped thermostat with the one from upstairs, still didn't work.
Can freely move fan on blower motor on inside unit (in attic) and outside unit.
Can physically push in "thingy" on contactor and unit comes on.
On inside unit, checked for 220 on one side of transformer... good. Checked for 24 on other side, no good. Compared this to the working unit for upstairs and it had 24v.
The next step I was thinking about doing was swapping the transformers but I'm going to wait till early morning when the attic has cooled off.
Is there anything else I should check or did I do my homework correctly? ;)
|
|
 |
Heating & Air Conditioning Expert
|
|
Sep 2, 2008, 03:44 PM
|
|
If 220 is going in 24 should be going out of the transformer.
|
|
 |
Ultra Member
|
|
Sep 2, 2008, 04:39 PM
|
|
The next step I was thinking about doing was swapping the transformers but I'm going to wait till early morning when the attic has cooled off.
Don`t bother,, unless you`ve a broken wire,just get a new transformer and replace the bad one
|
|
 |
Ultra Member
|
|
Sep 2, 2008, 04:52 PM
|
|
If you have a circuit board inside the inside unit you will a an auto type blade fuse. Check it to see if it has blown
|
|
 |
New Member
|
|
Sep 3, 2008, 10:30 AM
|
|
I've looked all over and haven't seen a fuse anywhere
|
|
 |
New Member
|
|
Sep 9, 2008, 04:06 PM
|
|
Update: I changed out the transformer, and while I am now getting 24v at the thermostat (multimeter actually says 28v, not sure if that's normal though), the thermostat makes a continuous clicking sound. As does the outside unit. And the unit never actually comes on. Any clue what's going on now?
|
|
 |
Heating & Air Conditioning Expert
|
|
Sep 9, 2008, 09:47 PM
|
|
24 or 28 it is all the same. You have low voltage now but are still having problems. You need to locate the low voltage signal circuit and repair it. The only real question you need to contend with is can you find that problem.
Did you change any wiring during your adventure?
Did you get a transformer large enough (supplying enough VA) to be able to activate your system? 40 VA minimum.
Have you checked the other components in the 24 volt circuit that could be causing the problem and probably burnt out the old transformer to start with?
Is it possible your system was hit by a voltage spike from the utility company? Have you experienced these in the past? Temporary high low voltage. (lights brite or dim) Brown out?
Check for loose or not well made connections in the complete 24 volt system.
The wiring and other problems will need to be solved by yourself with your meter or when all else fails call a qualified contractor and see what they can do.
|
|
 |
Uber Member
|
|
Sep 9, 2008, 10:18 PM
|
|
I'm suspecting an intermittant/loose connection with the 24 VAC. I would jump R to Y temporarily externally on the stat or at the furnace.
|
|
 |
New Member
|
|
Sep 9, 2008, 10:44 PM
|
|
Well I had low voltage. Whatever started clicking with the new transformer in seems to have killed that one too. Probably time for a pro.
|
|
 |
Heating & Air Conditioning Expert
|
|
Sep 9, 2008, 10:47 PM
|
|
Sounds like a short. This is probably what caused the other transformer to fail.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
24v transformer
[ 4 Answers ]
How do I wire up a 24v transformer in a furnace for thermostat? What does 24v & 24vA connect to? I have a problem of fusses blowing when I turn on the furnace.:confused:
How does heating transformer work?
24v transformer
[ 2 Answers ]
Need wiring diagram to wire in 24v transformer I have gas furnace and a regular condensing unit not a heat pump. Fan relay side is 120 v . Had old style fan relay which is no longer available was sold new trans with plug in fan relay. Wall thermo cycles condensing unit but blower fan in furnace...
Transformer
[ 1 Answers ]
I have a Goodman Heat Pump. The transformer in the air handler burnt out and I replaced it with one protected with a reset button. Now, when I use unit, I can only use in emergency heat. When I use in heat or cool mode it will trip the transformer in 30 seconds. Is this a low voltage problem? Air...
Transformer
[ 1 Answers ]
Hi guys
I'm having trouble finding a replacement transformer for my heating unit. The model number is AT140B1123. It's a Honeywell product but I can't find it on their website.
Thanks
Lou
Transformer
[ 5 Answers ]
How can you tell if you have blown a transformer? Also, does anyone know where I can find a part number for my transformer without being able to get to the part itself? I have a model number of 58PAV. The circuit board is HK42FZ009. I believe it is Carrier but not 100%