    kaczmaniandevil's Avatar
    kaczmaniandevil Posts: 4, Reputation: 1
    New Member
     
    #1

    May 3, 2008, 09:10 PM
    Romex wire/amp issue
    I am replacing a 30" kitchen range with a new 48". The existing wiring is approximately 30' of romex NM-B 8/3 on a 40 amp breaker. The new range requires as follows:

    Maximum connected load: 10.2 kW for
    48".
    Required power supply: 240V/208V/50A/60Hz for 48".
    Minimum supply wire size: L1 and L2 – 8
    AWG, neutral – 12 AWG, ground – 10 AWG
    For 48".
    Total electric rating: 10.2 kW at 240V, 8.8 kW at 208V for
    48".
    Total amps: 43 amps.



    Will the existing wire work for the new range with a new 50 amp breaker? Or do I need to upgrade to 6/3?

    Thanks in advance for any input.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 4, 2008, 04:53 AM
    You may leave the #8-3 Romex only if you leave the 40 amp breaker.

    Of course, you will not be able to use the range to it's fullest capabilities.

    To have a 50 amp fully rated circuit, you will need to install the #6-3 Romex.

    Now this may confuse the issue, but you may install #8-3 Metal Clad (MC) cable and use the 50 amp circuit breaker.

    You can compare the price difference between the #8-3 MC and the #6-3 NM-B.


    The reason is that NM-B cable is limited to using the 60 Deg C column of the NEC wire ampacity table #310.16, which is 40 amps. If something other than Romex is used, then #8 wire can use the 75 Deg C column, which is 50 amps max.
    kaczmaniandevil's Avatar
    kaczmaniandevil Posts: 4, Reputation: 1
    New Member
     
    #3

    May 7, 2008, 11:08 AM
    Thank you very much. You confirmed what I suspected. Excellent board and resource.
    sohard2c's Avatar
    sohard2c Posts: 5, Reputation: 1
    New Member
     
    #4

    Aug 26, 2008, 04:23 AM
    Not only Answered the Question but fully explained why. Extremely helpful to me on my project. Unfortunately, my work network blocks me from leaving a rating.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Stapling romex wire [ 11 Answers ]

How many romex wires (12/2, 14/2, 12/3, 14/3) can you staple by code? Can you staple 3 12/2 wires using one staple? Can you staple 3 14/2 wires using one staple. Thanks

Romex wire [ 2 Answers ]

Is Romex Wire Legal In New York City?

Hard wire 3 wire to 4 wire 220 service [ 1 Answers ]

How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?

Hard wire 3 wire to 4 wire 220 service [ 2 Answers ]

How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?

2 wire Single Stage Thermostat Issue [ 1 Answers ]

Thought this would be easy, Here is the problem, the furnace stays on all the time even thought the programmable themostat is set at a lower temperature than the room. The wiring must not be correct but there are only 2 wires. One for the transformer and one for the heat control. Please...


View more questions Search