    Hot tub wiring 4 wire 3 wire
    I have a 4 wire hot tub and have it wired to my 4 wire 60 amp gfci box outside, and it then goes into my basement where there is no 4 wire service. Do I connect the ground and neutral to the same location in the basement? :confused:
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Aug 25, 2008, 05:21 PM
    Quote Originally Posted by kory
    and it then goes into my basement where there is no 4 wire service. do i connect the ground and neutral to the same location in the basement ??:confused:
    WHAT does this mean?

    If your tub requires a neutral (4-wire circuit) then you MUST have a 4-wire circuit. NO way around it.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #3

    Aug 25, 2008, 05:52 PM
    Quote Originally Posted by kory
    i have a 4 wire hot tub and have it wired to my 4 wire 60 amp gfci box outside, and it then goes into my basement where there is no 4 wire service. do i connect the ground and neutral to the same location in the basement ??:confused:
    Kindof lost me as well? I'm going to assume you are asking do you terminate the grounding conductor, and neutral conductor on the same bar. The answer is no>>> if the wires are being terminated in a non-service rated panel. If the conductors are going to a sub-panel (non-service rated panel) then you should float the neutral and bond the equipment ground bar to the panel enclosure.
    kory's Avatar
    kory Posts: 5, Reputation: 1
    -
     
    #4

    Aug 25, 2008, 05:59 PM
    Quote Originally Posted by kory
    i have a 4 wire hot tub and have it wired to my 4 wire 60 amp gfci box outside, and it then goes into my basement where there is no 4 wire service. do i connect the ground and neutral to the same location in the basement ??:confused:
    I need to connect my 4 wire HOT HOT NEUTRAL GROUND in my basement in a 50 amp 240volt box, but there is on 3 wire there , what do I do with the extra 1 wire ( neutral )?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    Aug 25, 2008, 06:03 PM
    Whoa guys.

    The main panel may have bare and white (Neutral) terminated to the same bar. This is fine.

    There must be 4 wires red, black, what and bare/green going outside.

    The post could mean anything: 4 wires MUST run from hot tub box to basemant. Can't tell that explicitly from the OP's post.
    kory's Avatar
    kory Posts: 5, Reputation: 1
    -
     
    #6

    Aug 25, 2008, 06:10 PM
    So basically the ground and the neutral go to the same bar in the panel in the basement, the goes outside to my gfci box and the white goes to the neutral, the bare goes to ground and red and black go to the 2 hot terminals and so on though the tub.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #7

    Aug 25, 2008, 06:17 PM
    The main panel may have bare and white (Neutral) terminated to the same bar. This is fine.
    Where did this come from? Who said the OP was going to a main service rated panel?
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #8

    Aug 25, 2008, 06:19 PM
    so basically the ground and the neutral go to the same bar in the panel in the basement,
    Yeah, if this is your main panel.

    the goes outside to my gfci box and the white goes to the neutral, the bare goes to ground and red and black go to the 2 hot terminals and so on though the tub.
    sounds good to me!
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #9

    Aug 25, 2008, 06:22 PM
    Ok I see! I see what you mean Keep! The way it was written was confusing.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #10

    Aug 25, 2008, 06:25 PM
    Yes, but there are exceptions. You should either see two separate isolated bars with whites attached to one and bares attached to the other or whites and bares attached to the same bar (expected).

    The red and black go to a double pole breaker in the main panel. White goes to where the whites are attached but not to breakers. Bares go to where bares are attached.
    kory's Avatar
    kory Posts: 5, Reputation: 1
    -
     
    #11

    Aug 25, 2008, 06:31 PM
    I have a isolated neutral bar and a isolated ground bar in my gfci box outside along with the to hot connections. The same thing as in my hot tub control box. So I CAN connect the ground and neutral together in the breaker box in my basement? It is safe and correct?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #12

    Aug 25, 2008, 06:35 PM
    Yes, that's correct. Everything (hot tub panel, hot tub) which is past the main disconnect (main panel in your case) remains separate.
    kory's Avatar
    kory Posts: 5, Reputation: 1
    -
     
    #13

    Aug 25, 2008, 06:43 PM
    10/3 UF/B 4 wire

    BASEMENT BREAKER BOX: Ground and Neutral connected together at Ground Bar.
    Red and Black connect to the 2 hot spots.

    ::: Then I run the 4 wires outside to my GFCI 50 amp box

    OUTDOOR CFCI BOX: Connect white to isolated neutral Bare copper to isolated ground and red and black to 2 hot connections

    HOT TUB: Basically the same

    So this is corrrect? Thanks keepitsimplestupid
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #14

    Aug 25, 2008, 07:09 PM
    10/3 UF/B 4 wire
    The #10 is too small, if this is a hot tub.

    Kory, I hate to say this, but you may want to get some help! You are scaring me! There's much more to this install then you know. Example: You may have to run your conductors in conduit, because the manfacture may require a full sized EGC (EGC= equipment grounding conductor).
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #15

    Aug 25, 2008, 07:28 PM
    Just trying to help!
    Fr_Chuck's Avatar
    Fr_Chuck Posts: 81,301, Reputation: 7692
    Expert
     
    #16

    Aug 25, 2008, 07:45 PM
    Kory, you are not allowing emails so I am posting this here, most of your posts have been delted for various reasons, Please do not post insuting posts.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to wire 2 wire fan remote to 3 wire circuit? [ 10 Answers ]

I have a room that has 2 light switchs to the same light, so it is a 3 wire circuit. I bought a fan with a remote and the wall mounted remote has only 2 wires, how can I connect it? Thanks, Pete

Hard wire 3 wire to 4 wire 220 service [ 1 Answers ]

How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?

Hard wire 3 wire to 4 wire 220 service [ 2 Answers ]

How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?

3-wire home, 3-wire fan, 2-wire remote [ 9 Answers ]

Greetings, My home is 3-wire. I bought a Hunter ceiling fan (model 23811). The fan came with a remote assy. That I do NOT want to use... The fan has standard 3-wire connections (black, white, blk&white strip, ground). The remote receiver home-side wiring looks to be for 2-wire (blk and white)....

Wiring a 2 wire thermostat to a 4 wire system [ 1 Answers ]

I have a gas furnace equipped with central air.The compressor is shot in the AC unit,and I needed to replace the thermostat so I bought a heating only thermostat.I have the blower and the w wires together on the w terminal designation and the rh on the r terminal designation, and I have the y wire...


View more questions Search