Ask Experts Questions for FREE Help !
Ask
    paulcomi's Avatar
    paulcomi Posts: 2, Reputation: 1
    New Member
     
    #1

    Aug 16, 2008, 04:46 PM
    GFCI breaker wiring
    I hired someone yesterday to install a gfci on the circuit that my pool lights and small backyard office are on. My home has a GTE sylvania box which uses those zinsco breakers and the gfci breaker for this panel is almost $300 each. So he ran a small box next to it, powered the box off the 20amp circuit and after installing the gfci breaker fed the original pool light wiring off it. However he did it, it didn't work properly and the gfi tripped whenever the power was turned back on. He basically gave up because he couldn't figure out why it wasn't working and he restored the wiring like it was before, but I want to figure out the problem and asked him to give me a sketch of the wiring he was attempting to set up. Here's my interpretation of what he wrote down:



    Is there a problem with this set up that would cause the gfi circuit breaker to trip? Note that the 20 amp breaker that feeds the new small panel is not tripping.

    If there's nothing wrong with this wiring layout, I'll know that there is something else I need to track down.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Aug 16, 2008, 06:55 PM
    Well first of all a picture would really help us instead of a drawing. Second, why does it appear that there are two "Hot" leads coming from the GFCI breaker in the "B" or Sub panel.

    Did he jumper from the Breaker "B" ox back to the Main Panel? If he did, did he remove all of the connections from the existing lights in the Main Panel ans splice them to the Wires from the "B" box.

    The way a GFCI works is it monitors the difference of current between the Black (Hot) and the Neutral (Return) White. If there is a difference from 0.004 to 0.006 it will trip the breaker.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Aug 16, 2008, 07:31 PM
    From you drawing it doesn't look like either the GFCI or the circuit is connected to the neutral. Maybe its just your drawing.
    Why not just run a 20 amp circuit to the office, install a GFI outlet and let it protect the pool lights.
    Attached Images
     
    benaround's Avatar
    benaround Posts: 69, Reputation: 6
    Junior Member
     
    #4

    Aug 16, 2008, 10:39 PM
    Paul,

    The gfci breaker needs the factory white wire connected to the neutral bus, the drawing

    Does not show that connection.
    paulcomi's Avatar
    paulcomi Posts: 2, Reputation: 1
    New Member
     
    #5

    Aug 17, 2008, 12:21 AM
    Quote Originally Posted by donf
    Well first of all a picture would really help us instead of a drawing. Second, why does it appear that there are two "Hot" leads coming from the GFCI breaker in the "B" or Sub panel.

    Did he jumper from the Breaker "B" ox back to the Main Panel? If he did, did he remove all of the connections from the existing lights in the Main Panel ans splice them to the Wires from the "B" box.

    The way a GFCI works is it monitors the difference of current between the Black (Hot) and the Neutral (Return) White. If there is a difference from 0.004 to 0.006 it will trip the breaker.
    Here's a picture of the subpanel he added

    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #6

    Aug 17, 2008, 07:23 AM
    You need to temporarily remove the green and the pigtail and check continuity between the box and the bar. If there is continuity, then that will explain it not working.

    There is a screw between the two slots on the mounting bracket. I don't know if it's green or does it connect to the box. It could be a bonding screw and it would need to be removed if it is.

    Ground is provided by the armoured cable.

    I'd disconnect the white and the green that are connected to the bar and wirenut those two wires together. Should work if hypothesis is correct.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Aug 17, 2008, 07:50 AM
    Paul,

    As KISS indicated above, the Armored cable serves as the ground from the "B" panel to the Main Panel.

    Neutral (White) and Ground (Green) should only meet up at the Main Panel.

    Consider finding the green grounding screw or install a separate Grounding Bus. Although I do not see any screws in the "B" box to do this, but my image is not very clear.

    If I'm seeing it correctly, he brought over a 4 wire connection. Red is serving as the HOT Source for the "B" box bus. It should also be connected to the Circuit Breaker on the Main Panel. Neutral is properly connected to the Breaker and the Breaker is properly connected to the Neutral.

    The Black wire looks to be the Hot source Return to the Main Panel for connection to the wires going out to the lights.

    From your initial drawing, it appears as though there are two wires to the light branch circuit.

    Where is the Neutral that needs to be going to the lights?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #8

    Aug 17, 2008, 11:18 AM
    ..
    Attached Images
     
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #9

    Aug 17, 2008, 01:58 PM
    Guys, the armor does NOT provide a ground since that looks like MC cable. The only way it could is if that were HCF rated MC cable.

    That installation is NOT compliant! I see several issues.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #10

    Aug 17, 2008, 02:15 PM
    I see issues too: The major one being the use of green for neutral.

    What's the make and model of the sub-panel?
    benaround's Avatar
    benaround Posts: 69, Reputation: 6
    Junior Member
     
    #11

    Aug 17, 2008, 04:40 PM
    Paul,

    Can you send us a picture of the other panel, so we can see how it is tied in ?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring Hot Tub and using a 50 Amp Double Pole GFCI Circiut Breaker [ 10 Answers ]

:confused: I keep getting the GFCI breaker tripping after wiring my hot tub. I wired 2 hot Red and Black to the proper terminals and the White to the neutral and the Bare Copper to the ground Post at the tub. I am using 6-3 w/G per instructions. Could the GFCI breaker be bad? When I wire...

15 amp GFCI breaker popping [ 3 Answers ]

Hi, I have a GFCI breaker that pops when we vacuum in any room in the back of the house. Since we could be using 4 different plugs that pop the same breaker, would you start with the breaker? Also, would it be unwise to go to a 20 amp GFCI breaker :eek: ? Thanks Scott

Replacing GFCI Breaker With A Regular Breaker [ 1 Answers ]

I have a 15 amp circuit serving only a single outlet on my deck. It is protected by a GFCI circuit breaker in the home's single 125 amp service panel. I wish to replace the GFCI breaker with a regular 15 amp GE breaker. I will then protect the circuit with a GFCI outlet. I am familiar with...

GFCI Breaker vs Receptacle [ 1 Answers ]

I'm adding some 20A circuits in my garage/shop and know that they have to be GFCI protected. My question is this: Is there an advantage to using a GFCI breaker over just putting a GFCI receptacle in the first slot of the series? Thanks.

Gfci breaker [ 2 Answers ]

My question is I have a 50 amp GFCI breaker that I will be installing in the breaker box. I have another 50 amp GFCI breaker box that must be installed within 5 feet away from the hot tub. Is it OK to install both 50 amp GFCI breakers for this hot tub I realize I don't need two GFCI's but I...


View more questions Search