    Installing a sub panel
    I'd like to install a sub panel in my detached garage approximately 100 feet away.The previous owner ran 6/3 romex.Whats the largest amp sub panel I can use.He ran 6 gauge 3 wire with separate ground
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Aug 8, 2008, 02:37 AM
    35A, will give you a 2.8% drop at 120 V. Should be less than or = to 3%.
    Since the garage is detached, it should have a ground rod.
    Box can be rated higher and can optionally have a main breaker rated the same or higher (disconnect) as long as it's fed by a 35A breaker or less.
    Grounds and neutrals should remain separate in the sub. Sometimes an accessory ground bar kit is required.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Aug 8, 2008, 03:53 AM
    I have a differing opinion on this as KISS knows. :) ;)
    Where I differ is, at 100' voltage drop is not really an issue for a feeder such as this.
    Most electricians don't use 120v in figuring VD for a 120/240v feeder, and less than 3% is suggested for branch circuits but 5% is fine for final numbers and feeders.

    What I see wrong is you say "Romex". Is this typical indoor NM cable, or is it UF direct burial cable? Romex brand makes both kinds.

    If it is UF cable then you can use a 50A breaker and have a 120/240v feeder.
    If it is indoor NM cable you CANNOT use it at all.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Installing a ne Main Panel [ 11 Answers ]

I am changing the location of the meter and I decided to install a new main panel and rewire the existing one as a sub-panel keeping all the existing brakes at their place I am going to use an SER 600V cable to connect the 2 panels. My question is: How am I going to connect the SER cable at the...

Wiring from my house panel to my pole barn panel [ 1 Answers ]

I am going to be wiring my pole barn up soon and just need some help on the type of wire to use. In my house I have a 200 AMP service and plan on running a 100 AMP feeder from that panel to my subpanel in the barn. (Just under 100 Feet) I am going to run a 6 gauge ground, two 4 gauge...

Breaker size in main panel to support sub panel? [ 7 Answers ]

Hello, I am wiring a sub-panel to the outside of my home (50 feet from main 200 amp box). I ran 3 wire - 6 gauge. What is the largest 2 pole breaker I can put in the main panel to supply the sub-panel. TYPE NM-B 6-3 WITH GROUND 600 VOLTS CIRTEX-I EZ-STRIP (R) PLUS 17:11 2/5/07 SB/RC ...

Installing second service panel [ 1 Answers ]

QUESTION: I am finishing off my basement and would like to add a service panel box in the basement. I have a 200amp panel box in my garage with 11 open slots out of 32. The builder pre wired a wire from the panel to the basement. The wire has a orange shield with #10 wire. There are 4 wires (3 and...

Installing a 60 AMP sub panel for a work shop [ 1 Answers ]

I have a 200 AMP main panel for my residence with all the breaker slots filled. I plan on removing 2 20 amp breakers and installing a 1 60 x 2 20 amp consolidated breaker in to the panel. Well at least I am told I can do this. I plan on having 2 240 VAC 30 amp breakers in the shop (one will have...


View more questions Search