    AC breaker
    The unit trips the breaker. It doesn't do it all the time, but more then not. The specs on the back of the unit state min/max 45/60 amp. The old unit only used a 30 amp. Can I replace the 30 amp with a 45/50 amp without burning down the house or causing other electircal issues?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jul 21, 2008, 04:53 PM
    So are you saying the old unit was replaced but the wiring was not??

    If the new unit calls for a 45A breaker minimum what wold posses the installer to keep the 30??

    You need to tell us the "Minimum circuit ampacity" and the "Maximum fuse or breaker size".

    Not "min/max, 45/60". Be specific.

    If the minimum circuit ampacity really is 45 amps then a strong NO, you cannot simply increase the breaker size. You MUST run a new circuit.
    While you're at it find another A/C guy.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Jul 21, 2008, 06:49 PM
    A pair of #6's, and 10 for ground would work on 50 or 60 Amp Breaker.
    If it was 30 Amps, wiring may need upgrading. Don't put On a Breaker larger than the wire can handle.
    If existing wiring was #6, you Lucked out.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Replacing GFCI Breaker With A Regular Breaker [ 1 Answers ]

I have a 15 amp circuit serving only a single outlet on my deck. It is protected by a GFCI circuit breaker in the home's single 125 amp service panel. I wish to replace the GFCI breaker with a regular 15 amp GE breaker. I will then protect the circuit with a GFCI outlet. I am familiar with...

Replacing Circuit Breaker with Higher AMP Breaker [ 8 Answers ]

Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...

New 15A breaker trips main 100A breaker [ 6 Answers ]

Hi, I've been finishing my basement and I added a few 15A breakers One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets. When installing the drywall I accidentally shorted the outlet closest to the panel. It...

Can I switch a 15 amp breaker to a 20 amp breaker? [ 1 Answers ]

:confused: can I switch a 15 amp breaker to a 20 amp breaker? I just bought a home tanning bed and the plug has a horizontal plug which won't fit in a regular outlet. I bought a 20 amp outlet and installed it. The tanning bed tripped the circuit breaker. I got a 20 amp circuit breaker and replaced...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!


View more questions Search