Ask Experts Questions for FREE Help !
Ask
    taneal1953's Avatar
    taneal1953 Posts: 13, Reputation: 1
    New Member
     
    #1

    Jun 25, 2008, 10:06 AM
    AWG requirement for long wire run
    Hi, I'm planning to replace my tank-type water heater with a tankless model.

    Electrical specs: 60a dp c/b; #6 AWG wire; 11.8kw; 54a max @220v

    Available voltages: 208v/220v or 240v/277v

    QUESTION #1: Why the range of voltages for each option rather than just 220v (voltage
    Drop due to wire length)?


    My installation requires a 90' wire run, which will cause a noticeable voltage drop.

    QUESTION #2: How do I determine whether #6 wire is acceptable, or will I need #4?

    THANKS for any info!

    Tom
    rsain2004's Avatar
    rsain2004 Posts: 207, Reputation: 6
    Full Member
     
    #2

    Jun 25, 2008, 10:24 AM
    My understanding is larger wire will reduce voltage drop during in-rush, and the ampacity is also dependent on the type of insulation on the wire... heat under load...

    Talk to the dealer of the water heater. The different voltage ranges may be how the heating elements are wired... wye or delta, a schematic would illustrate that.

    Be safe...
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Jun 25, 2008, 10:39 AM
    Tom,

    The cable formula I used set the cable at a #5 sized wire.

    My concern is that I have not proven the accuracy of this formula yet, so please wait for verification from other responders.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Jun 25, 2008, 11:19 AM
    Q!: The manufacturer has to specify the voltages that the appliance will operate at. 208, 277 and 240 are common voltages. If you had a motor, for instance, if it did not say 240V, you could not operate it at 240 V. Residential voltages are now 240/120, not 110/220.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Jun 25, 2008, 11:21 AM
    Tom,

    I left some information. You would be using 240VAC. 220 is no longer furnished to a household. The available voltages for household are 120 and 240.

    Guessing that you would be using 6/3 (I wasn't sure if you would just need 240 VAC or a combination of 120/240)

    I calculated using 6/3, which adds an extra conductor to the mix. I also use the value of 12 to identify the conductor type of copper. I figured you would prefer copper over aluminum.

    Any way, #6/3 works out to 7.4%. The max you are allowed is 7.2? For 240.
    that why I went to #5/3 which brought the voltage drop down to 5.4%.

    I'll run it through at 6/2 just on the possibility that you only need 6/2 cable.

    If you are using just 240, I get a number of approximately 6% using #6/2 cable.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #6

    Jun 25, 2008, 11:30 AM
    Q2: Using 240V, 59A, 90', Copper, #6 gives a 2.2% drop.
    taneal1953's Avatar
    taneal1953 Posts: 13, Reputation: 1
    New Member
     
    #7

    Jun 25, 2008, 11:57 AM
    Don,

    Thanks for your response!

    Yes on the copper, 240v only, and 6/2 (two hots + ground) wire.

    < The max you are allowed is 7.2? For 240. >
    I see your question mark after 7.2 - does the max voltage drop vary per local code?

    < just 240, I get a number of approximately 6% using #6/2 cable. >
    Apparently, #6 would be OK if 7.2 is the max...

    If you don't mind, could you run the same calculations for a larger heater?
    It requires two separate lines. Each line requires 240V; 40A c/b; #8/2 wire. The total is 18 kw; max load 77amps at 240v.

    Would #8 copper be adequate for the same 90 foot run?

    Again, thanks VERY MUCH for this info!

    Tom



    Thanks,

    Tom
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #8

    Jun 25, 2008, 02:35 PM
    Tom,

    The NEC restricts conductors to specific amperages. #8 is for 40 amp max. So no, it cannot be used for a 60 amp line.

    However, please review KISS' posting that yielded a 2.X voltage drop for 60 amp 2 wire copper size 6 AWG.
    taneal1953's Avatar
    taneal1953 Posts: 13, Reputation: 1
    New Member
     
    #9

    Jun 25, 2008, 03:11 PM
    Don,

    < The NEC restricts conductors to specific amperages. #8 is for 40 amp max. So no, it cannot be used for a 60 amp line. >
    This calculation would be for a different model heater. *EACH* of the TWO separate #8 lines would carry only a 40 amp load - not 60 amps.

    See quote below.
    <It requires two separate lines. Each line requires 240V; 40A c/b; #8/2 wire. The total is 18 kw; max load 77amps at 240v. >
    This is the way the specs are listed by the manufacturer. I presume the total kw and max amp load numbers refer to the load SHARED by the two lines.

    Tom
    taneal1953's Avatar
    taneal1953 Posts: 13, Reputation: 1
    New Member
     
    #10

    Jun 25, 2008, 03:16 PM
    Thanks, KISS!

    Quote Originally Posted by KeepItSimpleStupid
    Q2: Using 240V, 59A, 90', Copper, #6 gives a 2.2% drop.
    So, you're saying that with the 5.28v drop the #6 wire is adequate?

    Tom
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #11

    Jun 25, 2008, 06:38 PM
    Yep.

    Don's calculation was in volts. Not %. We are shooting for <3%.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #12

    Jun 25, 2008, 08:08 PM
    For your other Q: #8, 90', 240 V, copper, 39 A (~77 A/2) = 2.3% drop, OK
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #13

    Jun 25, 2008, 08:36 PM
    Note I took 54 A/220 V = x A/240 V since the relationship is linear and got x = ~59A for your first case.

    You don't have to derate the cable by multiplying the current x 1.25 since the load is not continuous (more than 3 hrs at a time in a day).
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #14

    Jun 26, 2008, 06:49 AM
    Tom,

    Where in the devil did the second heater come from? Did I miss something?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #15

    Jun 26, 2008, 08:42 AM
    Donf: You must be aging way to fast. In post 7:

    If you don't mind, could you run the same calculations for a larger heater?
    It requires two separate lines. Each line requires 240V; 40A c/b; #8/2 wire. The total is 18 kw; max load 77amps at 240v.
    So, I divided the 77/2, I was to lazy, so I used 78 and got an even number. Assumed load was shared equally between both services and checked Vd for #8 copper.

    Still trying to convince donf that his formula is wrong.
    taneal1953's Avatar
    taneal1953 Posts: 13, Reputation: 1
    New Member
     
    #16

    Jun 26, 2008, 03:53 PM
    Quote Originally Posted by KeepItSimpleStupid
    Note I took 54 A/220 V = x A/240 V since the relationship is linear and got x = ~59A for your first case.

    Thanks for the formula! I was planning to ask. You are (at least) one step ahead of me.

    You don't have to derate the cable by multiplying the current x 1.25 since the load is not continuous (more than 3 hrs at a time in a day).
    That's good to know. I wasn't thinking about factor.

    THANKS to you KISS and to DonF, also!

    Tom
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #17

    Jun 26, 2008, 07:20 PM
    Why would you use an electric tankless water heater? They are not efficient, they rarely work well and they are huge enegy hogs... as you know by the wiring requirements.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #18

    Jun 26, 2008, 08:09 PM
    He has 12 kids and they all take 30 minute showers, I guess.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #19

    Jun 27, 2008, 04:59 PM
    Doesn't the water heater require TWO 220 volt circuits, 4 breakers? I recently installed one and it needed 2 two pole breakers.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #20

    Jun 28, 2008, 08:26 AM
    MB,

    You can not get 220 VAC for households any more. You can only get 120/240.

    You use two breakers because each 120 VAC will be 240 VAC apart. This is the normal way to convert 120 VAC to 240 VAC. This is what you do for water heaters, furnaces and the like.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to wire 2 wire fan remote to 3 wire circuit? [ 10 Answers ]

I have a room that has 2 light switchs to the same light, so it is a 3 wire circuit. I bought a fan with a remote and the wall mounted remote has only 2 wires, how can I connect it? Thanks, Pete

Long distance subpanel wire size [ 7 Answers ]

I have a horse barn that is 1014 feet of 1.5" conduit away from the main house panel. The main panel is 400 amp 240/120 volt and I have left 100 amps for use in the barn. My current electrical needs in the barn are 2 - 1/2hp motors, one for a gate and one for a hot walker, and a small fridge that...

SPA disconnect switch grounding wire requirement [ 1 Answers ]

I'm installing a 240V/60A SPA approximately 85 feet from the house service panel. I'm going to run 3 individual #6 conductors (THN or better) from the service panel to the SPA GFI disconnect box via 1 inch PVC conduit. The SPA is about 7 feet from the disconnect box. The disconnect box instructions...

Hard wire 3 wire to 4 wire 220 service [ 2 Answers ]

How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?

3-wire home, 3-wire fan, 2-wire remote [ 9 Answers ]

Greetings, My home is 3-wire. I bought a Hunter ceiling fan (model 23811). The fan came with a remote assy. That I do NOT want to use... The fan has standard 3-wire connections (black, white, blk&white strip, ground). The remote receiver home-side wiring looks to be for 2-wire (blk and white)....


View more questions Search