    115v arc welder tripping 20amp breaker
    I just bought a Arc Welder that can use 220 or 115 but since the only 220v outlet is the dryer inside the house I had to choose the 115v mode. I have it plugged in inside the garage on a 20 amp breaker. The manual said no to go above 70v on a 30 amp breaker. The job I need requires all 70v and when I get going for a few minutes welding the breaker trips.

    Would upgrading the breaker to 30amp keep the breaker from tripping, or would installing a 220v outlet without destroying the walls and stuff work better?

    I would prefer 220v but I don't want to destroy the walls. The breaker panel is in the garage also.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jun 27, 2008, 01:55 PM
    Increasing the breaker to 30 amps is NOT an option.

    Run it within the guidelines at 120v, or install a 240v circuit for it.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Jun 27, 2008, 03:07 PM
    Switcher,

    What Stan is telling you is that the size of the conductors govern the amount of ampcity of the conductor.

    NEC code provides these rules:

    The current running through a conductor is limited to 15 Amps for #14 AWG cable. A #12 gauge is used for 20 Amps and a #10 AWG gage is for 30 Amp conductors.

    If you try to run 30 amp through at listed 20 amp conductor, you may start melting the insulation on the conductors or cause a fire.

    Pulling the cable, should not be all that difficult. You remove the receptacle on the outlet area. At the main panel, cut power off, then find the end of the run that breakers to the room. Connect the new cable and use the old wire to pull the new right through to the panel box.

    PLEASE, if you believe that no do not that the experienced enough to do this you need to get a qualified electrician in to do the work.

    Since the current level of voltage in household is either 120 or 240, not 110 or 220. Since you are going to have to run new conductors for your welder, you might as well use #10 AWG with 240 volts and a new 240 VAC outlet.

    The higher voltage will help the welder operate better.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Breaker for AC Tripping [ 3 Answers ]

I have a split system & Air Handler. Any idea why the breaker keeps tripping?

15AMP Breaker used instead of 20AMP -ok? [ 4 Answers ]

We just had an electric gate installed that extends across our driveway. I noticed that the installer used a 15 amp breaker switch to connect to for power (the gate is the only device on this breaker). In looking at the manual last night the installation instructions call for a 20 AMP breaker (the...

Switching from 15AMP breaker to 20AMP [ 6 Answers ]

I am contemplating switching my 15AMP breaker into a 20AMP breaker because the lights flicker in my home office because my computer and printer eat up a lot of power. If I switch breakers, will this help my power problem? Or I am limited to the gauge of the wires in the wall? Thanks for the...

Adding a 20amp receptacle to a 15amp breaker [ 2 Answers ]

Hi All, I need to install a small tankless water heater (made for under the lavatory sink) for the sink in my bathroom. The specs on the water heater are: 120 Volts, 2.4kW, 20 Amps, wire size: 10AWG. My question is this... The existing bathroom outlet that I want to splice into to add this water...

20amp circuit breaker, 15 amp receptacles [ 2 Answers ]

I have a 20amp circuit breaker with 15 amp receptacles and light switches on #12 wire with a load of 1700, is this allowable? If not, and I change to a 15 amp circuit breaker, is the 1440 watt safety load in the code or is it a non-code safety suggestion?


View more questions Search