    Install 200amp subpanel from 400amp main panel
    Building a new home. The detached garage has a 400amp service panel which is hardly used (has 2 20amp breakers for garage lights). I want to install a 200amp panel in the house basement which is located about 100 feet from the garage panel.

    I have purchased and installed the 200amp panel in the house basement. What is the best way to now connect the 200amp panel to the 400amp panel. I have installed smaller amperge subpanels previously but do not seem to find any 200amp breakers to do this same function within the 400amp main panel.

    Thank you.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    May 17, 2008, 03:53 AM
    Let me get this straight. You have a single 400A panel in the garage? For just the garage?
    What else is this feeding?
    How is the house being fed?

    You will likely not find a 200A branch circuit breaker. Most panel busses have a maximum branch circuit rating of 100 or 125 amps.
    U079310's Avatar
    U079310 Posts: 5, Reputation: 1
    New Member
     
    #3

    May 17, 2008, 04:05 AM
    [QUOTE=stanfortyman]Let me get this straight. You have a single 400A panel in the garage? For just the garage?

    Yes Stan you have this correct. The 400A panel is just for the garage. The guy who built the garage was eventually planning on building a home but sold to me before he did so. The 400A panel currently has (2) 20A breakers just for garage lighting.

    The home I mentioned is new, there is nothing providing power to it now. That is the purpose of the 200A panel I purchased for the home basement.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    May 17, 2008, 04:44 AM
    Ahhhh. So the garage was existing, the home is new-new. Got it.

    Well, like I said, it is rare to have a typical panel that will accept a 200A branch breaker.
    I would go to a supply house and give them the model number of the panel and see what branch circuit breakers are available for it. A home center will be useless for this.

    In the meantime post that info here and we'll can see what we come up with.

    You'll need a 2" or 2.5" conduit and 4/0AL or 2/0CU wire to feed this panel.

    Also, where is the phone and cable coming from?
    And what code cycle are you under for electrical?
    These are important questions.
    U079310's Avatar
    U079310 Posts: 5, Reputation: 1
    New Member
     
    #5

    May 17, 2008, 04:57 AM
    Have already checked for breaker possibilities on the GE 400A main panel. The largest breaker available is 100A.

    I live in Michigan so my handout from the County inspector says that they enforce "Michigan State Electrical Code 2002 which includes the NEC Code 2002".

    Phone and cable in a separate trench in from the road, no problems there. This may be stupid but could you take (2) 100A breakers and run 1 hot wire from each to the lugs on the 200A panel in the house ?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    May 17, 2008, 05:13 AM
    This is what I do NOT like about using a 400A panel in a residential setting. They are foolish IMO.
    With two 200A panels in parallel you could have replaced one with a feed-through panel and sent 200A to the house.
    Your situation is one of the drawbacks of using a single 400A panel.



    Quote Originally Posted by U079310
    This may be stupid but could you take (2) 100A breakers and run 1 hot wire from each to the lugs on the 200A panel in the house ?
    Well, not a stupid question, but NO you certainly cannot do that.


    I hate to say this, but without seeing the actual setting, I'm not sure what I'd do in your situation. Replacing the 400A panel with two 200's is looking like the easiest thing to me.
    It might actually be cheaper and easier still to simply bring a new 200A service to the house from the road.
    Maybe you can open a machine shop in the garage to take advantage of the awesome service out there?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #7

    May 17, 2008, 01:05 PM
    Check out the I-line distibution panels from squareD.

    http://ecatalog.squared.com/pubs/Ele...0120BR9202.pdf

    At least you'll be able to distribute power properly.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    May 17, 2008, 05:44 PM
    I-Line? In a residence?? :eek:
    Heck, by the time you buy just the panel and breakers you could install a whole new 200A residential service at the house.
    Handyman2007's Avatar
    Handyman2007 Posts: 988, Reputation: 73
    Senior Member
     
    #9

    May 17, 2008, 08:08 PM
    Why not remove the 400 amp from the garage, relocate the service to the house (200amp) then run a separate 60 amp sub panel to the garage? That is the simplist way as far as I am concerned. I am surpised that the utility co even allowed a 400amp service just in a garage without any building plans for a house first??

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire type from main panel to adjacent subpanel [ 1 Answers ]

I have a 200 amp main panel that is nearly full and I plan on adding a 100 amp subpanel close by in the basement of my residence (south-east PA). I happen to have some wire available that I believe is adequate gauge (based on reading many other posts) but I want to make sure the specific wire I...

Wiring of a 200AMP main panel - SEU wires entry point [ 3 Answers ]

Hello, I am putting a new 200AMP main panel in a service upgrade. Its location is a little higher than the meter socket. The panel and the meter are back to back on a wall (meter outside, panel inside). Main disconnect is at the top of the panel, as are the connections for the SEU cable. Can I...

Convert Main Panel to Subpanel? [ 3 Answers ]

After rough-wiring my old house to a new 200 amp Main Panel (wired-in but not yet connected to the service line and still using the original 100 amp fuse-type panel) I've decided to build a major addition that makes the originally planned service entrance a poor location. Question: Can I...

Main panel as subpanel [ 2 Answers ]

Hello: I stumbled across your forum and found a question that was close to mine, but have a more detailed query. I am wiring a shop/apartment. The building has a 200 amp service panel. The main loads (a/c, range) and dedicated loads (fridge, smoke detectors, etc) are branch circuits on the main...

Subpanel or main service panel? [ 4 Answers ]

Hello, I want to put a subpanel in my shop, and was wondering if a main service panel that they sell at say Home Depot is the same thing as a subpanel? I have a 200 amp service to my house, and want to put a 100 amp subpanel in my shop. Does the term "subpanel" just mean that it is wired off the...


View more questions Search