  • Nov 23, 2013, 08:20 AM
    Abrun44
    What size aluminum triplex?
    I want to deliver 50 amps to my well sight using direct burial triplex aluminum. It is 625' from existing power. What size wire should I use?
  • Nov 23, 2013, 08:43 AM
    stanfortyman
    Too many variables to answer right now.

    What are you powering? Just the well?
    Why 50A?
    What does the well draw?

    625' is a very long way to go with 120/240V. Is there any closer source?
  • Nov 23, 2013, 10:23 AM
    ma0641
    Even at a 20 Amp draw, #6 Aluminum shows:
    Voltage drop: 15.57
    Voltage drop percentage: 6.49%
    Voltage at the end: 224.43
    #4Aluminum At 50 Amps is worse:
    Voltage drop: 24.49
    Voltage drop percentage: 10.20%
    Voltage at the end: 215.51
    Closest to 5% loss is 1/0 AWG
    Why is the well so far away? 625 ft. is not going to be easy without a pole and transformer.