  • Mar 6, 2007, 10:48 PM
    Alessio
    UPC - Use of Tees in Horizontal vent
    Anyone:
    Where a vertical vent meets a horizontal vent in a Tee, does the code require a San-Tee?

    TIA
  • Mar 7, 2007, 12:35 AM
    nmwirez
    Quote:

    Originally Posted by Alessio
    Anyone:
    Where a vertical vent meets a horizontal vent in a Tee, does the code require a San-Tee?

    TIA

    You can use a combo, even a wye with various els... Short Santees have less of a gradual bend into the horizontal run. Some snakes do not pass the bend for easy cleanout. Nm
  • Mar 7, 2007, 07:33 AM
    iamgrowler
    Quote:

    Originally Posted by Alessio
    Anyone:
    Where a vertical vent meets a horizontal vent in a Tee, does the code require a San-Tee?

    TIA

    It does require a Sanitary-Tee.

    Do not confuse a San-Tee with a Vent-Tee, though. A Vent Tee is a straight tee with no built in venturi allowing for direction of flow -- They are sold all along the West Coast in the big box stores, but are expressly forbidden for use by the UPC.
  • Mar 7, 2007, 07:36 AM
    iamgrowler
    Quote:

    Originally Posted by nmwirez
    you can use a combo, even a wye with varous els....Short Santees have less of a gradual bend into the horizontal run. Some snakes do not pass the bend for easy cleanout. nm

    With the UPC's more stringent clean out requirements, snaking through a vent is less of a concern.