Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   THHN THNN wire designation (https://www.askmehelpdesk.com/showthread.php?t=684745)

  • Jul 19, 2012, 02:44 PM
    shader
    THHN THNN wire designation
    Is the THHN and THNN designation equivalent, or is there even a THNN designation?

    Due to convience I ordered wire over the internet- THHN. The lable indicates THHN but the wire marking indicates it is THNN. It also has the usual THWN-2 marking. I can't find the THNN designation in NEC table C.1. The wire is Southwire produced on 4/8/11, the Southwire site makes no reference to THNN, and a web search reveals nothing. Any ideas?
  • Jul 19, 2012, 03:34 PM
    stanfortyman
    There is no THNN. If it says this it is a typo of sorts.
    Most all newer THHN wire is dual rated THWN, so what you have it normal.
  • Jul 19, 2012, 03:48 PM
    shader
    Stan,
    I figured a typo error since all of the other specs (MTW, gas/oil resistant, etc) check out, but wasn't totally sure if I was missing something. Maybe that's why the wire was reasonalby priced.