I have a grounded 2.5 ton compressor and want to put a 2 ton compressor in it's
Place. Wil it work?
![]() |
I have a grounded 2.5 ton compressor and want to put a 2 ton compressor in it's
Place. Wil it work?
So you don't want to swap a 2ton straight ac condenser with a 1.5 condenser? What's going to happen if you do and how long will it last. And where is this talented hvac
[QUOTE=craig136;3126691]so you don't want to swap a 2ton straight ac condenser with a 1.5 condenser? What's going to happen if you do and how long will it last. And where is this talented hvac { Craig which is it 2 1/2 to 2 ton compressor or 2 to 1 1/2? In any event you would loose about less than 6000 BTUH of cooling. "What will happen" is you will most likely have reduced comfort levels. Why do you want to down size your A/C system? }
Rule of thumb--- Its OK to have your evaporator coil a 1/2 ton larger than the compressor. Never opposite. Make sure the compressor is rated for the same refrigerant of the system you now have(R22 or 410a)