  • Mar 30, 2012, 04:10 PM
    GregGowing
    Keep rite furnace hi eff
    T-stat calls for heat, no inducer until I remove a wire off any limit. Than inducer turns on, but no hot surface. Checked continuity on all limits there all good I am stumped. Replaced mother board because of a ground short. I'm confused, any suggestions
    Greg
  • Mar 30, 2012, 07:02 PM
    T-Top
    To me it sounds like your thermostat is wired wrong or is bad. You can wire R to W at the thermostat and see if the heat will work. If it works it's a bad thermostat or set up wrong. If it doesn't work you can use a wire and jumper R to W at the control board of the furnace if that works your thermostat wire is bad.
  • Mar 30, 2012, 09:33 PM
    GregGowing
    All ready jumped r n w together and nothing, that's why I'm confused