-   -   I have an armstrong sx ultra 80 gas furnace the pilot is lit but the burners will no (https://www.askmehelpdesk.com/showthread.php?t=623488)

  • Dec 30, 2011, 11:22 AM
    vspeight
    I have an armstrong sx ultra 80 gas furnace the pilot is lit but the burners will no
    I have an armstrong sx ultra 80 gas furnace the pilot is lit but the burners will only come on when I take the door off till they light and then I put the door back on once the temp reaches the level on the thermostat it will shut off it will not come back on when the temp drops until I go and do the process all over again
  • Dec 30, 2011, 01:52 PM
    wmproop
    Where is the furnace located? something has happened to cause the furnace to not get enough air

    It won`t hurt to leave the door off,as long as there nothing close by that is flameable, JUST until you can get more info as how to fix, I`ve seen people run them for years with no door, as long as the door that covers the blower compartment is closed
  • Dec 30, 2011, 04:46 PM
    vspeight
    My furnace is located in the basement. Where is the blower compartment. Cause the door I have to take off is the one on top where the pilot and the burners are located
  • Dec 30, 2011, 06:05 PM
    mygirlsdad77
    Can you post some pics of your furnace and furnace vent, along with the top furnace cover (which you have removed)?
  • Dec 30, 2011, 11:07 PM
    wmproop
    The blower compartment is on the opposite end