-   -   Is there anywhere in the NEC that allows flexible cord to be installed in a raceway? (https://www.askmehelpdesk.com/showthread.php?t=617760)

  • Dec 7, 2011, 03:00 PM
    ASHIKAGA
    Is there anywhere in the NEC that allows flexible cord to be installed in a raceway?
    Is there anywhere in the NEC that allows flexible cord to be installed in a raceway?
  • Dec 7, 2011, 03:14 PM
    tkrussell
    Cord is only allowed to be in raceway in very specific locations or reasons, such as from the 2008 Edition of the NEC:

    501.140 Flexible Cords, Class I, Divisions 1 and 2.
    (A) Permitted Uses.
    (B) Installation.
    Where flexible cords are used, the cords shall comply with all of the following:

    (3) For electric submersible pumps with means for removal without entering the wet-pit. The extension of the flexible cord within a suitable raceway between the wet-pit and the power source shall be permitted.


    So, need to know exactly what your application is.