Coleman DGAA070BDTA furnace heat problem
Furnace is installed in a trailer without central air.(heat only) Trailer had been unoccupied with heat turned down very low. Went to work @ trailer and heat worked fine. When I left, again turned heat down. Went back a week later and heat would not come on. T-stat called for heat, ignigtor lit, combustion fan runs and burner lights, blower fan comes on for short time and burner goes out. Fan continues to run for short time and shuts off. This cycle will repeat several times. Replaced t-atat and filters are clean. Same problem. Any idea what might be wrong?
Comment on mygirlsdad77's post
Thank you! By the glow plug I assume you are referring to the ignigter? Is there any cautions to removing the burner assembly to acess the flame sensor?
Comment on mygirlsdad77's post
Thanks again! Your direction was right on and everything is working fine. I appreciate your valuable help.