    Furnace is installed in a trailer without central air.(heat only) Trailer had been unoccupied with heat turned down very low. Went to work @ trailer and heat worked fine. When I left, again turned heat down. Went back a week later and heat would not come on. T-stat called for heat, ignigtor lit, combustion fan runs and burner lights, blower fan comes on for short time and burner goes out. Fan continues to run for short time and shuts off. This cycle will repeat several times. Replaced t-atat and filters are clean. Same problem. Any idea what might be wrong?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Feb 13, 2011, 10:55 AM

    Sounds like the flame senser may be dirty. Try cleaning it with steel wool, sandcloth, or fine sandpaper. Careful not to touch or bump the glow plug as they are very fragile and break easily. The flame senser will be located on the opposite side of the glow plug on the burner. Just the metal rod that sticks in front of the flame.
    JFactor's Avatar
    JFactor Posts: 3, Reputation: 1
    New Member
     
    #3

    Feb 13, 2011, 03:00 PM
    Comment on mygirlsdad77's post
    Thank you! By the glow plug I assume you are referring to the ignigter? Is there any cautions to removing the burner assembly to acess the flame sensor?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #4

    Feb 13, 2011, 03:39 PM

    Yep, by glow plug, I mean the hot surface igniter. As for removing the burner assemly, make sure gas is off, all wires are disconnected(igniter, flame senser, and gas valve. Should be a total of five wires. Then, when actually taking out the burner, just be very careful not to let the igniter hit anything. Other than that, just remember the gas valve orientation and placement of wires when reinstalling. Most likely you have a flex gas supply. If this is the case, then you don't need to disconnect the gas line. However, if it is hard piped, you will need to break the union to remove the gas valve(turn gas off either way). Good luck and let me know if this cures the problem.
    JFactor's Avatar
    JFactor Posts: 3, Reputation: 1
    New Member
     
    #5

    Feb 16, 2011, 04:48 PM
    Comment on mygirlsdad77's post
    Thanks again! Your direction was right on and everything is working fine. I appreciate your valuable help.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #6

    Feb 16, 2011, 05:27 PM

    Glad to hear you got it fixed. Thank you for the update.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Coleman furnace problem [ 5 Answers ]

I have a customer with a DLAS075 furnace. It takes way too long for it to heat up enough to close the fan switch. I am leaning toward the booster assembly but I am not sure. My thought is that the burner is not getting enough air to make the fire hot enough. The gas pressure is correct and nothing...

Coleman furnace problem [ 3 Answers ]

I have a coleman electric furnace its in our 2003 mobile home we bought new. It is clicking click click and if you'll check the coming out of vent it will get cooler then it will click click click and the heat over the vent will get hot again I've replaced sequencher, all limit switches.Did not...

No heat coleman evcon furnace [ 1 Answers ]

Topic: None Chosen Your Question: "i have a coleman furnace model dgat056bdd i have replaced the ignitor and the sensor rod the combustion blower is ok the centrifugal is ok and the blower is ok too but this is what it is doing for heat it turns on the combustion blower turns on for about 30...

Coleman electric furnace/heat pump. When elec heat comes on, it will not shut off. [ 1 Answers ]

Last week when I got up for work I noticed the house warmer than normal. I found the electric heat strips still energized. Tstat was set for 70 house was 74. I do hvac work but deal with air handlers, chillers and small boilers, only residential when its mine. Anyway, I asked the guy at Johnstone...

Coleman furnace problem [ 1 Answers ]

I have a 1989 Coleman direct vent (sealed combustion system) forced air furnace equipped with standing pilot Model 7665-856 Serial 048272343 This problem only occurs when it is really cold outside. When I need the furnace the most. The furnace starts up normally. Burner turns on then fan...


View more questions Search