    tableclocks
    Pressure cked OK... limit switck cked OK
    No one seens to be helping me unless there all out this w/e... o well...
    Rheem rgph 10eamer... 1000,000... 80%... 3 blimks and a 2 second pause says the limit is open... it cked OK with 0 ohms
    Pressure switch cked OK with 0 ohms
    Blower fan stays running unless I turn off the main power
    I have no spark.. direct spark ignitor, therefor I have no gas comeing on or no heat...
    Fan stays on with the a/c on also...
    Please help if you can... thanks... richard
  • Sep 19, 2010, 11:26 AM
    mygirlsdad77

    You may have more than one high limit. Look on or near the blower housing(not draft inducer, but main blower housing). Many times there is a limit that is resetable along with the one that resets itself. This limit will usually have a small button in between two spades/wires. Hope this helps.
  • Sep 19, 2010, 12:06 PM
    tableclocks

    Thank you... thank you... thank you yes I found it
    Took it off
    Power off
    B to y.. open
    Y to w.. open
    B to w.. closed...
    You think this is my proublem??
    Thanks... richard
  • Sep 19, 2010, 12:09 PM
    tableclocks
    Quote:

    Originally Posted by mygirlsdad77 View Post
    you may have more than one high limit. Look on or near the blower housing(not draft inducer, but main blower housing). Many times there is a limit that is resetable along with the one that resets itself. This limit will usually have a small button in between two spades/wires. Hope this helps.

    No reset pins... thank you thank you thank you
    Took it off... power off..
    B to y... open
    Y to w... open
    B to w.. closed
    Think its bad or another what to ck it
    Thank you... richard
  • Sep 19, 2010, 12:13 PM
    mygirlsdad77

    I think you may be looking at the transformer, not the limit I was thinking of. The limit I'm thinking of would have only two wires going to it, be roughly the size of a dime or a little smaller.
  • Sep 19, 2010, 12:23 PM
    mygirlsdad77

    If you can't find another limit, try this. Shut power to furnace off. Then go back to the high limit you tested and jump the two wires that are hooked to it together. If this solves the problem, do not under any circumstances use the furnace with the wires jumped. Get a replacement limit as soon as possible.
  • Sep 19, 2010, 12:27 PM
    tableclocks

    One limit at the heat exchanger... 2 wires... its 170... 20... cked OK... 0 ohms
    2nd limit on the blower motor size of size dime... 4 wires... held on w 2 small screws
    47-22860-03 part # thank you

    Dinner at a all you can eat place if you get to balto md... tks... richard
  • Sep 19, 2010, 12:34 PM
    mygirlsdad77

    Okay gotcha. You will need to look at your wiring diagram on the inside of the blower door to see which two wires are in the limit circuit. Then you can jump them two wires to bypass limit for testing purposes only. If furnace works, replace that limit. Keep me posted.
    And yes, I'm betting this limit is your problem.
  • Sep 19, 2010, 12:44 PM
    tableclocks

    Tks... I,m so wore out now... testing and testing... I,ll need a brake and look at it later... thank you so very much... I will keep you posted... thank you... richard..
    I'll have to figure out how... to figure out how to figure out whitch 2 are for the limit etc... w and one of the blues are jumped... or purple... I,m colored blind... some colors... lol... thank you
  • Sep 19, 2010, 01:09 PM
    mygirlsdad77
    Let me know if this is right. You have two yellows hooked onto one spade. Across from that you have a white on one spade, and also the white is jumped to one of the blues. Then across from that blue is a single blue. If so, jump the blue/white, to the other blue. This will bypass the limit. If the furnace works now, shut it back down and replace the limit asap. Hope this works. I finally remembered that I have a rheem 80 percenter in my home, so I went a took a look and I believe I have the same limit as you. I looked at the wiring diagram and this is what I came up with. Jumping the blues will bypass the limit, its okay to leave the white hooked up when doing this. Good luck, and please keep me posted.
  • Sep 19, 2010, 02:10 PM
    tableclocks

    Yes
  • Sep 19, 2010, 02:13 PM
    tableclocks

    Yes... thats what I have... if I junp the be and w that's on 1 spd to the other b... should it be the same if I junp the single be to the w..
    Because the w is already junped to the b
    All 24 volts? I'll stay on line till I get your answer... tks
  • Sep 19, 2010, 02:15 PM
    mygirlsdad77

    Yep, you can jump white to single blue
  • Sep 19, 2010, 02:20 PM
    tableclocks

    The b/w and the single b read 0 ohms... closed... with the furnace off..
    Should be open
  • Sep 19, 2010, 02:23 PM
    tableclocks

    Trying it now... if I live I'll post you in 20 or so... tks
  • Sep 19, 2010, 02:31 PM
    mygirlsdad77

    Wait, if you don't feel comfortable jumping, then don't. Its hard for me to truly trouble shoot this online. I would really like to be able to help you, but it may be in your best interest to call in an onsight pro. Wish I could be there to help, but, well, you know. I just don't want to have you do anything your not comfy with, and possibly do harm to yourself or your equiptment. Wish you the best, and still glad to hear how things go.
  • Sep 19, 2010, 02:45 PM
    tableclocks

    Junping did not help maybe more then 2 have to be junped... I tried to find on line how to ck this switch... no results,, if your tired of fooling with me... I understand... thanks very much for your help... if you think of something else... I,ll try it... tks... richard
    1 yellow and single b goes to the gas vaule
    Other be and why goes to a 9 pin on the board...
    Maybe junp the be and y... at the gas vaule?
  • Sep 19, 2010, 02:49 PM
    tableclocks
    Quote:

    Originally Posted by mygirlsdad77 View Post
    Wait, if you dont feel comfortable jumping, then dont. Its hard for me to truly trouble shoot this online. I would really like to be able to help you, but it may be in your best interest to call in an onsight pro. Wish i could be there to help, but, well, you know. I just dont want to have you do anything your not comfy with, and possibly do harm to yourself or your equiptment. Wish you the best, and still glad to hear how things go.

    I was kidding about still being alive... I can do this... I just don't know what to ck... I always do safety and turn the furnace off... ect... I wired my whole house... going to school as soon as it opens for heating... I got my unaversial lisenc for a/c... but really no on thb stuff... all book stuff...
  • Sep 20, 2010, 03:37 PM
    tableclocks

    I switched back to heat on the therm from air and went down to ck some 24 volt aeras... looking to see if the I F U was fried... when I got down there... the furnace was lighting as if nothing was wrong... so maybe I jiggled something...
    Of the preasure switch and the 2 limit switches... that put the furnace in motion... one of then is proubly working and not working at times... 2 other times last winter I had the some systoms but the furnaced worked after just jiggling around... possiable that one of the limit switches can work and not work at times..? Or is dead usually dead? Thank you for your help... richard
  • Sep 20, 2010, 03:49 PM
    mygirlsdad77

    Just glad its working now. I got to thinking about the lower limit and its just for the gas valve, I don't think it would cause the blower to stay on all the time. just shuts the gas off. And yes, limits can sometimes work and sometimes not, but usually when they are bad, they are bad. Hope it works for a long time to come. Take care.

    Sorry about the late response.