Have a 5 ton air handler with a 4 ton condenser. Off my supply plenum I have 3-6", 1-9" and 1 10" flex runs I know they are too small. Will replaceing the 9 and 10" runs with 2-12" runs be enough so I don't restrick this handler
![]() |
Have a 5 ton air handler with a 4 ton condenser. Off my supply plenum I have 3-6", 1-9" and 1 10" flex runs I know they are too small. Will replaceing the 9 and 10" runs with 2-12" runs be enough so I don't restrick this handler
Thanks, I did light service work long time ago but not much duct work. Got some attic work to do!
One more question, I'm way undersized in the supply ducts. Will that cause the 24 degree temp drop I'm getting and some frost on the suction line?
Thanks, borrowed a leak detector, no leaks found, thought the airflow restriction might be the cause. Didn't notice this summer with 95+ degrees every day.