    If a stair has more than 6 treads where is lighting required?
  • Sep 7, 2010, 11:28 PM
    Clough
    Hi, spiduki1123!

    Why are you asking the question, please? It would be helpful to know that. Perhaps this might be concerning something that needs to be according to a certain code?

    Don't know...

    Thanks!
  • Sep 8, 2010, 08:38 PM
    spiduki1123
    Hi Clough:
    Thanks for your response I got the question on a home inspector's test; my answer was - at the top and bottom of the stair, however I have no way to know if I'm correct. Yes, I do believe it is a code relating question, but does not know which.

    Thanks for your help
  • Oct 11, 2011, 09:17 PM
    richsah
    Did you ever find the answer to this question?
    If not the answer is in the middle. http://www.inspectapedia.com/interiors/Stair_Codes.htm
  • Jun 5, 2012, 04:16 PM
    RBMCCORMICK
    Correct answer from Nachi


    Illumination:
    •Lighting at the stairs is needed. All interior and exterior stairways should have a means to illuminate the stairs, including both the landings and the treads. Correction and further evaluation is recommended.
    •Lighting at the landings is needed. Interior stairways should have a light located at each landing, except when a light is installed directly over each stairway section. Correction and further evaluation is recommended.
    •There are missing controls for the lights at the stairway. Interior stairways with at least six risers require wall switches at each floor level, unless the lights are continuously illuminated or automatically controlled. Correction and further evaluation is recommended.

    Blake
    Florida Hom Inspections


    From InterNACHI's advanced tips for inspecting stairways and sample reporting language (U.S.-only version). - InterNACHI http://www.nachi.org/stairwaysusonly.htm#ixzz1wxk8Qgam
  • Jun 5, 2012, 04:17 PM
    RBMCCORMICK
    I apologze all

    Here is theanswer without the highlights easier to read..

    There are missing controls for the lights at the stairway. Interior stairways with at least six risers require wall switches at each floor level, unless the lights are continuously illuminated or automatically controlled.

    Blake
    F.H.I.
  • Jun 5, 2012, 04:18 PM
    RBMCCORMICK
    Inter Nachi specs:

    Interior stairways with at least six risers require wall switches at each floor level, unless the lights are continuously illuminated or automatically controlled.