I have 8 volts on a neutral wire at one of my recepticals is this within tolerances
![]() |
I have 8 volts on a neutral wire at one of my recepticals is this within tolerances
I will assume you measured 8 volts between neutral and equipment ground.
No, we look for a maximum of 3 volts.
Some equipment will not want more than 1/2 to one volt.
This can be tricky to locate, could be a ground loop, could be a loose or corroded connection.