I am hooking up a hot tub rated for a 50 amps max fuse size. I already have the #8 thhn and 1/2 liquid tight flex conduit. Will the #8 wire be enough for 50 amps.
![]() |
I am hooking up a hot tub rated for a 50 amps max fuse size. I already have the #8 thhn and 1/2 liquid tight flex conduit. Will the #8 wire be enough for 50 amps.
Yes, #8 copper THHN is good for 50 amps.
I question the 1/2" flex.
Most tubs that I know of need 4 wires, in this case 3-# 8 THHN and 1 - #10 THHN for the equipment ground.
If the whip is short you may not have any problems fitting the wiring in the flex.
Subpanel needs a 4 wire also, otherwise what is is the 4 wire branch circuits, so your plan is flawed.