  • Apr 27, 2010, 04:13 PM
    terry53
    Central heat pump condenser fan motor do not work
    Fan motor works only for about 30 minutes and shuts off. Compressor continues to run. Fan motor usually restart within 3-4 hours later or the next day. I can sometimes use a stick to get motor going. Is this a motor problem or a capacitor problem?
  • Apr 27, 2010, 04:16 PM
    bigdaddy51

    Sounds like time for a new motor if the cap was bad the motor would'nt start