  • Apr 10, 2010, 10:50 AM
    vintagelaser
    a/c thermostat has no power
    My central thermostat(dizital) has no power
  • Apr 10, 2010, 11:01 AM
    vintagelaser
    a/c thermostat has no power
    a/c thermostat has no power. There is no battery on the thermostat unit, what should I check? Can it be bad thermostat? Ut side breaker is been reset
  • Apr 10, 2010, 12:36 PM
    Joshdta

    If you have no power to the stat and now battrie then the furnace is not sending 24 volts to the stat.
  • Apr 12, 2010, 10:09 AM
    vintagelaser

    Thanks, I took stst out from the wall and between Blue and red line reads 26 on the meter, it's that mean I am getting 24 volt from the furnace and can be a bad stat?
  • Apr 12, 2010, 03:53 PM
    Joshdta

    Yes you have voltage to the stat. if blue is on c

    Put a jumper form r to g and see if the fan comes on
  • Apr 12, 2010, 06:12 PM
    vintagelaser

    OK... thanks for your help. I will try that, what if fan comes on? That means the faulty stat?

    What if fan doesn't turn on?
  • Apr 12, 2010, 06:40 PM
    Joshdta

    You can test r to g for fan
    R to w for heat
    R to y for cool

    If all works you need a new stat. if they do not work then you have other problems we will have to figure out
  • Apr 12, 2010, 11:45 PM
    vintagelaser

    Thanks, I replace a stat and it worked. Thanks again