    50 A sub panel
    I have a 200A main Load Center. Can I install a 50 A circuit Breaker in the main LOAD CENTER and use for a sub panel a GE load center of 100 A( 12/24).
  • Jan 25, 2010, 06:36 PM
    hermanwachs

    Yes. Use 6/3 cu and separate the neutral and ground at the subpanel.