    dconstant
    I have a heil furnace and replaced a skuttle spray type humidifier. After the install
    After installing a skuttle spray type humidifier and testing it o.k. I closed the panels and went to the thermostat to retest. When I call for heat from the thermostat, nothing happens. The blower fan won't even turn on.
  • Jan 23, 2010, 12:17 PM
    wmproop
    Is possible you fried the transformer during the new install,, does anything work,, the ac maybe?
  • Jan 23, 2010, 01:10 PM
    dconstant
    The doesn't work either.
  • Jan 23, 2010, 01:13 PM
    dconstant
    The ac doesn't work either.
  • Jan 23, 2010, 01:26 PM
    wmproop
    I would check the transformer for power output after checking to make sure there is power to the furnace, check all fuses and breakers
  • Jan 23, 2010, 02:48 PM
    dconstant
    Transformer has 110 going in but 000 on the 24vac output side.
  • Jan 23, 2010, 06:13 PM
    dconstant
    I don't understand why the blower (operates off 110vac) doesn't work. If the transformer is fried then only the 24vac side shouldn't work.
  • Jan 23, 2010, 06:45 PM
    T-Top

    24 volts tells the blower relay to work. Are you sure you got your humidistat wired right?
  • Jan 23, 2010, 07:33 PM
    dconstant
    I replaced an old one with a new one and wired it the same.