  • Dec 9, 2009, 08:50 AM
    jwl0606444
    National electric code free online
    What's the distance for gfci from water fixture?
  • Dec 9, 2009, 08:55 AM
    tkrussell
    Zero to 72 inches from a sink.

    Why is your post title different than your question?
  • Dec 9, 2009, 08:58 AM
    donf

    Anywhere within a 6 ft. radius of water an outlet must be protected by a GFCI receptacle. That receptacle can protect just itself or other receptacles that are downstream of it.

    Also, a GFCI circuit breaker can protect the entire branch-circuit.
  • Dec 9, 2009, 09:32 AM
    stanfortyman

    The term "water fixture" does not appear in the NEC.
  • Dec 9, 2009, 09:34 AM
    stanfortyman
    Quote:

    Originally Posted by donf View Post
    Anywhere within a 6 ft. radius of water an outlet must be protected by a GFCI receptacle.

    This is simply not true Don. There are locations, such as laundry and wet bar, where there is a 6' proximity to a sink, but "water outlet" is not a term
  • Dec 9, 2009, 09:55 AM
    donf

    Stan,

    I did not use the term, "Water Fixture".

    I used the term,"Water" because I was thinking in terms of a bathroom where sinks, showers or tubs would be present.
  • Dec 9, 2009, 10:05 AM
    stanfortyman

    Like I said, the only 6' numbers are laundry, utility and wet bar.

    Kitchens are ALL counter 120v 15 & 20 amp receptacles.
    Outside, bathrooms, unfinished basements & crawls, garages, sheds, out buildings, are all 120v 15 & 20 amp receptacles.
  • Dec 9, 2009, 11:10 AM
    donf

    Stan,

    Allow me to retrench a little bit. The Residential Wiring book shows a 6' radius from water, but it is showing the installation of a lighting track. Not that that is code applicable.

    I did re-check the 2008 NEC section 210.8 A [ all 125 volt 15 and 20 amps shall have GFCI protections as in sections 1 through 8. (1) Bathrooms.

    So as I interpret it to say that if there is a branch-circuit going into a bathroom whether it is for a light fixture or not, it needs to be on a GFCI protected circuit.

    The words "Water or Water fixture" are not relevant if it is a Bathroom.
  • Dec 9, 2009, 11:36 AM
    stanfortyman
    Quote:

    Originally Posted by donf View Post
    Allow me to retrench a little bit. The Residential Wiring book shows a 6' radius from water, but it is showing the installation of a lighting track. Not that that is code applicable.

    Then I see where the misconception lies. Those books are not nearly always right.



    Quote:

    Originally Posted by donf View Post
    I did re-check the 2008 NEC section 210.8 A [ all 125 volt 15 and 20 amps shall have GFCI protections as in sections 1 through 8. (1) Bathrooms.

    So as I interpret it to say that if there is a branch-circuit going into a bathroom whether it is for a light fixture or not, it needs to be on a GFCI protected circuit.

    No, because 210.8(A) is for receptacles, not branch circuits:
    (A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel.



    Quote:

    Originally Posted by donf View Post
    The words "Water or Water fixture" are not relevant if it is a Bathroom.

    "Water or Water fixture" are not relative anywhere. About the only related term would be "sink".
  • Dec 9, 2009, 03:48 PM
    donf

    Stan,

    Back to the source book (2008 NEC Handbook) I went.

    As quoted by you, section 210.8A reads as you say.< Not that I am surprised at all.>

    That makes my statement "All branch circuits going into a bathroom..." wrong. The correct response is that any Receptacle in a bathroom "Shall" be protected by a GFCI. Also any circuit that serves both a bathroom lighting fixture as well as a receptacle would also need GFCI. Given that GFCI is protection for humans and not necessarily the branch-circuit equipment.

    I have got to be more reticent in reading the code. Slow down and think, not speed read.

    Thanks for the corrections it is most appreciated.
  • Dec 10, 2009, 11:14 AM
    tkrussell
    Always read the Code slow, and carefully.

    Quote:

    Originally Posted by donf View Post
    Slow down and think, not speed read.

    Always be sure you understand where you are in the Code, as Sections before are important and may be related, and any that may be referred to in the Section you are reading.

    Each word in the Code is very important.
  • Jul 13, 2012, 12:35 AM
    wvoyl8
    How close must a swimming pool filter be to the electrical outlet. This filter hangs from the side of the pool.
  • Jul 13, 2012, 07:36 AM
    tkrussell
    The filter can be as close as necessary to the outlet, however, the outlet cannot be closer to the pools edge than 10 feet if using a standard GFI protected receptacle, or 6 feet if the outlet is a single, grounding, locking device, and of course, GFI protected.
  • Aug 6, 2012, 01:22 PM
    jlw6710
    Is it OK to have the GFCI plug in on the wall that is in front of the sink about 3 feet away from the sink and about 2 ft away from the door
  • Aug 6, 2012, 01:23 PM
    jlw6710
    How many GFCI plug ins do you have to have over top of the kitchen sink? Is there a certain distance that the GFCI plug ins have to be away from each other. My husband has 3 GFCI above the sink, is that OK or can we do it a safe cheaper way? Thanks for you help
  • Aug 6, 2012, 01:25 PM
    jlw6710
    He says he knows but I am just making sure. That's just me. We bought a home and flipped it. What is some other things about residential wiring that you can tell me. I just want to learn. I find electrical wiring interesting. Thanks
  • Aug 6, 2012, 03:42 PM
    hkstroud
    Quote:

    Is it OK to have the GFCI plug in on the wall that is in front of the sink about 3 feet away from the sink and about 2 ft away from the door
    Yes.
    I assume you mean over a kitchen counter. Wouldn't make much common sense to put it directly over the sink.

    Quote:

    Is there a certain distance that the GFCI plug ins have to be away from each other.
    No, can be as close as you would like.

    Quote:

    My husband has 3 GFCI above the sink, is that OK or can we do it a safe cheaper way?
    You could put in one GFI outlet and have it protect the other two non-GFI outlets.

    Quote:

    I just want to learn.
    It is outlet or receptacle not plug. A plug is the thing on the end of your lamp cord that you plug into the outlet.

    It is GFI (Ground Fault Interrupter) outlet not GFCI.

    It is a GFCI (Ground Fault Circuit Interrupter) circuit breaker. They go in the breaker panel and interrupt the entire circuit. They provide GFI protection to the entire circuit.

    Don't get mad, you asked.

    Ask all you questions in one post, not necessary to post each question separately. Don't piggy back (tack your question on to someone else's thread).

    Welcome to AMHD. A great place to get help.