    National electric code free online
    What's the distance for gfci from water fixture?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 9, 2009, 08:55 AM
    Zero to 72 inches from a sink.

    Why is your post title different than your question?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Dec 9, 2009, 08:58 AM

    Anywhere within a 6 ft. radius of water an outlet must be protected by a GFCI receptacle. That receptacle can protect just itself or other receptacles that are downstream of it.

    Also, a GFCI circuit breaker can protect the entire branch-circuit.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Dec 9, 2009, 09:32 AM

    The term "water fixture" does not appear in the NEC.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Dec 9, 2009, 09:34 AM
    Quote Originally Posted by donf View Post
    Anywhere within a 6 ft. radius of water an outlet must be protected by a GFCI receptacle.
    This is simply not true Don. There are locations, such as laundry and wet bar, where there is a 6' proximity to a sink, but "water outlet" is not a term
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Dec 9, 2009, 09:55 AM

    Stan,

    I did not use the term, "Water Fixture".

    I used the term,"Water" because I was thinking in terms of a bathroom where sinks, showers or tubs would be present.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Dec 9, 2009, 10:05 AM

    Like I said, the only 6' numbers are laundry, utility and wet bar.

    Kitchens are ALL counter 120v 15 & 20 amp receptacles.
    Outside, bathrooms, unfinished basements & crawls, garages, sheds, out buildings, are all 120v 15 & 20 amp receptacles.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #8

    Dec 9, 2009, 11:10 AM

    Stan,

    Allow me to retrench a little bit. The Residential Wiring book shows a 6' radius from water, but it is showing the installation of a lighting track. Not that that is code applicable.

    I did re-check the 2008 NEC section 210.8 A [ all 125 volt 15 and 20 amps shall have GFCI protections as in sections 1 through 8. (1) Bathrooms.

    So as I interpret it to say that if there is a branch-circuit going into a bathroom whether it is for a light fixture or not, it needs to be on a GFCI protected circuit.

    The words "Water or Water fixture" are not relevant if it is a Bathroom.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #9

    Dec 9, 2009, 11:36 AM
    Quote Originally Posted by donf View Post
    Allow me to retrench a little bit. The Residential Wiring book shows a 6' radius from water, but it is showing the installation of a lighting track. Not that that is code applicable.
    Then I see where the misconception lies. Those books are not nearly always right.



    Quote Originally Posted by donf View Post
    I did re-check the 2008 NEC section 210.8 A [ all 125 volt 15 and 20 amps shall have GFCI protections as in sections 1 through 8. (1) Bathrooms.

    So as I interpret it to say that if there is a branch-circuit going into a bathroom whether it is for a light fixture or not, it needs to be on a GFCI protected circuit.
    No, because 210.8(A) is for receptacles, not branch circuits:
    (A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel.



    Quote Originally Posted by donf View Post
    The words "Water or Water fixture" are not relevant if it is a Bathroom.
    "Water or Water fixture" are not relative anywhere. About the only related term would be "sink".
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #10

    Dec 9, 2009, 03:48 PM

    Stan,

    Back to the source book (2008 NEC Handbook) I went.

    As quoted by you, section 210.8A reads as you say.< Not that I am surprised at all.>

    That makes my statement "All branch circuits going into a bathroom..." wrong. The correct response is that any Receptacle in a bathroom "Shall" be protected by a GFCI. Also any circuit that serves both a bathroom lighting fixture as well as a receptacle would also need GFCI. Given that GFCI is protection for humans and not necessarily the branch-circuit equipment.

    I have got to be more reticent in reading the code. Slow down and think, not speed read.

    Thanks for the corrections it is most appreciated.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #11

    Dec 10, 2009, 11:14 AM
    Always read the Code slow, and carefully.

    Quote Originally Posted by donf View Post
    Slow down and think, not speed read.
    Always be sure you understand where you are in the Code, as Sections before are important and may be related, and any that may be referred to in the Section you are reading.

    Each word in the Code is very important.
    wvoyl8's Avatar
    wvoyl8 Posts: 1, Reputation: 1
    New Member
     
    #12

    Jul 13, 2012, 12:35 AM
    How close must a swimming pool filter be to the electrical outlet. This filter hangs from the side of the pool.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #13

    Jul 13, 2012, 07:36 AM
    The filter can be as close as necessary to the outlet, however, the outlet cannot be closer to the pools edge than 10 feet if using a standard GFI protected receptacle, or 6 feet if the outlet is a single, grounding, locking device, and of course, GFI protected.
    jlw6710's Avatar
    jlw6710 Posts: 3, Reputation: 1
    New Member
     
    #14

    Aug 6, 2012, 01:22 PM
    Is it OK to have the GFCI plug in on the wall that is in front of the sink about 3 feet away from the sink and about 2 ft away from the door
    jlw6710's Avatar
    jlw6710 Posts: 3, Reputation: 1
    New Member
     
    #15

    Aug 6, 2012, 01:23 PM
    How many GFCI plug ins do you have to have over top of the kitchen sink? Is there a certain distance that the GFCI plug ins have to be away from each other. My husband has 3 GFCI above the sink, is that OK or can we do it a safe cheaper way? Thanks for you help
    jlw6710's Avatar
    jlw6710 Posts: 3, Reputation: 1
    New Member
     
    #16

    Aug 6, 2012, 01:25 PM
    He says he knows but I am just making sure. That's just me. We bought a home and flipped it. What is some other things about residential wiring that you can tell me. I just want to learn. I find electrical wiring interesting. Thanks
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #17

    Aug 6, 2012, 03:42 PM
    Is it OK to have the GFCI plug in on the wall that is in front of the sink about 3 feet away from the sink and about 2 ft away from the door
    Yes.
    I assume you mean over a kitchen counter. Wouldn't make much common sense to put it directly over the sink.

    Is there a certain distance that the GFCI plug ins have to be away from each other.
    No, can be as close as you would like.

    My husband has 3 GFCI above the sink, is that OK or can we do it a safe cheaper way?
    You could put in one GFI outlet and have it protect the other two non-GFI outlets.

    I just want to learn.
    It is outlet or receptacle not plug. A plug is the thing on the end of your lamp cord that you plug into the outlet.

    It is GFI (Ground Fault Interrupter) outlet not GFCI.

    It is a GFCI (Ground Fault Circuit Interrupter) circuit breaker. They go in the breaker panel and interrupt the entire circuit. They provide GFI protection to the entire circuit.

    Don't get mad, you asked.

    Ask all you questions in one post, not necessary to post each question separately. Don't piggy back (tack your question on to someone else's thread).

    Welcome to AMHD. A great place to get help.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Free/Almost Free Online Multiplayer Games [ 51 Answers ]

Hi all, Just wondering if anyone could recommend any free/nearly free online multiplayer games. A few friends and I are looking for some good games over the internet. Preferably something other than a MMORPG as you have to devote a lot of time to those in order to keep up with each other. ...

Reading the NFPA 70 etc. National Electric Code Online [ 1 Answers ]

It does seem impossible to search for, but just about any code published by the NFPA is readable online. You will have to register for a username and password. The NFPA 70: National Electrical Code starts here: NFPA 70: National Electrical CodeŽ Near the bottom af the page there is a...

National code questions for livingroom wiring [ 4 Answers ]

Hi there everyone, 20a circuit & 12ga wire: I'm wiring a living room (14x18). Am I correct in my interpretation that I require only two circuits, one for the outlets and one for outlets/lighting? I ask because in a kitchen application, lighting was not to be on any of the appliance...