  • Oct 15, 2009, 06:20 AM
    ruddle
    Nordyne Heat Furnace Blower
    I have a Nordyne heater in a 1996 mobile home. My A.C. works normal. I can also switch the blower to ventilate and it works normal. But, when I switch the thermostat to heat. The blower will not come on. I can see the furnace heating up, but that it. According to the diagram, this unit does have 2 sequencers. Please help.
  • Oct 15, 2009, 09:30 AM
    hvac1000
    If this is an electric unit the heat sequencers could control the blower in the heat mode but some Nordyne electric units have used a small circuit board. Refer to your wiring diagram on the unit.
  • Oct 15, 2009, 09:45 AM
    ruddle

    Yes, this is a electric heater. Are the sequencers easy to replace? Are they bolted in position?
  • Oct 15, 2009, 09:52 AM
    hvac1000
    First they usually have a lot of electric wires on them so you better know exactly what you are doing. They are usually bolted or screwed into the metal mounting area.

    If you mess up the wiring you will be toast.
  • Oct 15, 2009, 09:57 AM
    ruddle

    Thanks for the advice. I'm am not reast to meet my maker just yet. Therfore, I will have to call a repairman. Thanks
  • Oct 15, 2009, 10:16 AM
    hvac1000
    No problem