  • Aug 15, 2009, 12:26 PM
    kalebson
    White rodgers 1F85-0471
    I am replacing my old thermostat, the wiring is as follows:

    Green wire > g terminal
    Blue wire > y terminal
    White wire > w terminal
    Red wire > r terminal

    There is a jumper between the r's as well

    I am replacing this with a white-rodgers 1F85-0471.. which I can not contact on Saturday.. thought might get some help here

    Should I use the same terminals on the white rodgers? The wiring diagram in the installation instructions are very vague. Appreciate any help.
  • Aug 15, 2009, 12:45 PM
    hvac1000
    Use the same color wires on the same lettered terminals on the WR stat.

    The only strange one is the blue on the Y terminal so I guess they just used the blue instead of the yellow color.
  • Aug 15, 2009, 12:59 PM
    kalebson
    Quote:

    Originally Posted by hvac1000 View Post
    Use the same color wires on the same lettered terminals on the WR stat.

    The only strange one is the blue on the Y terminal so I guess they just used the blue instead of the yellow color.

    Thank you. Yes it seems odd but there is no yellow wire in the 4 wire harness. Blue is connected to Y on the board in the exchange unit as well.