  • Jun 17, 2009, 09:51 PM
    lostnspace
    Coleman a/c troubles again
    Okay I don't have the funds to call a repair man so here I am. I've got a coleman central air unit that has had a lot of upgrades (new circuit board latest). I turned the air on and it was blowing room temp air. I went outside to see if the fan was working and it wasn't. So I tried turning the thermostat up above room temp. then I went outside took off the access panel and watched while I had wife turn the temp. down. Inside blower works fine but not a damn thing on the unit itself no hum nothing. I am very reluctant to press in on the contactor with a screwdriver so I didn't. Any other suggestions to help would be greatly appreciated.(Detailed please)
  • Jun 18, 2009, 06:46 AM
    dac122

    First check to see if you have power to the unit on that circuit, and if the control wires are okay.
  • Jun 18, 2009, 11:19 AM
    lostnspace
    Okay so how do I go about testing it specifically.
  • Jun 18, 2009, 01:58 PM
    dac122

    For power, check for 220VAC power at the box and also at your contactor.

    For control wires, if you have a control board check for 24VAC to the board. For a simple A/C system with 2 wires, simply check continuity on the two wires.