-   -   Replacing a 3 ton 10 seer AC with a 3.5 ton 10 seer (https://www.askmehelpdesk.com/showthread.php?t=356169)

  • May 20, 2009, 04:55 PM
    effex1
    Replacing a 3 ton 10 seer AC with a 3.5 ton 10 seer
    Can I use the existing evaporator or would I need to replace the evaporator coil


    How about using a 4 ton 10 seer unit
  • May 20, 2009, 05:12 PM
    mygirlsdad77

    You can keep the existing a-coil if you size the orafice correctly, or have a txv valve. However, it is best practice to have the a-coil and condernser matched. I would also suggest having a minimum 13 seer installed(coil and condenser), as ten seers is a thing of the past.
  • May 20, 2009, 07:03 PM
    dac122

    Just curious why are you up-sizing the outdoor unit? I also agree you should jump to a 13 SEER unit.
  • May 20, 2009, 08:23 PM
    wmproop
    I`m guessing you are replacing the 3 ton with a used 3.5 ton condenser,, around my state there are no more new 10 seers units to be had
    If this is the case you won`t have a warranty to worry about,because the condenser and evap coil don`t match