  • Mar 8, 2009, 03:51 AM
    suniljayarajan
    Starter panel
    I want to make a starter panel for 3 Kw

    So what should be the rating of MCCB, contactor, and OLR

    How can I find out its rating of the above mentioned

    If the supply voltage is 220v ac
  • Mar 26, 2009, 03:17 AM
    sarnian
    Hello suniljayarajan

    For current calculation it is important to know if it is star or delta wiring.
  • Apr 18, 2009, 09:15 AM
    sathe1963

    Dear Sunil,

    Your equipment is 3 kw at 220 v ac. Hence motor current would be @ 13.6 Ampere at full load.
    You would require 10 to 16 ampere MPCB, instead of MCCB. Contactor range available is 18 ampere. LC1D18 of merlin gerin make.