  • Mar 1, 2009, 09:31 PM
    suniljayarajan
    Chart for lugs according to wire size
    I want to ask where I will get the lug for the proper wire size or core cable
    If it shows how much amps it will carry in a single chart
    Otherwise tell me in which site I will get it
  • Mar 1, 2009, 09:44 PM
    KISS

    I don't understand the question:

    Lugs typically accept a wire size and have a hole that can be used to attach it to a bus. Like #10 wire with a #8 stud.
  • Mar 2, 2009, 01:43 AM
    suniljayarajan
    I mean when we 70mm wire den what lug we should use
    For 4mm, 6 mm
    Like that
    So to compare the leg with the wire or cable
    Also d need all dimension of lug
  • Mar 26, 2009, 03:40 AM
    sarnian
    Hello suniljayarajan

    Standard cable lug sizes are :
    1.5 mm , 2.5mm , 4mm , 6mm , 10mm , 16 mm2 , 25mm2 , 35mm2 , 50mm2 , 70mm2 , 95mm2 , 120 mm2 , 150 mm , 185 mm2 , 240 mm˛ , 300mm2 , 400mm , 500mm .

    Wire size to max. current :

    0,50 mm˛ = 3A
    0,75 mm˛ = 6A
    1,00 mm˛ = 10A
    1,25 mm˛ = 13A
    1,50 mm˛ = 16A
    2,50 mm˛ = 20A
    4,00 mm˛ = 25A
    6,00 mm˛ = 40A
    10,0 mm˛ = 63A
    16,0 mm˛ = 80A
    25,0 mm˛ = 100A
    35,0 mm˛ = 125A
  • Mar 30, 2009, 12:51 AM
    suniljayarajan
    Thank you for your reply

    U have mention the wire size and amps

    But I meed lug size and amps

    Once again thanking u
  • Apr 18, 2009, 10:45 PM
    sathe1963
    Dear sunil,

    Lugs sizes are independent of current carrying capacity. They are prominently termed with reference to cross section area i.e. Mm2 size of conductor. Cord lugs, dowells, jainson are the reputed manufacturer of the lugs. (cross section area i.e. Mm2 is selected on the basis of current in ampere of the load.)
  • May 25, 2012, 10:36 AM
    anil_aniljal
    Sis wire lug size
  • May 25, 2012, 10:43 AM
    tkrussell
    Please re-state your question, use more words to describe what you need.
  • May 26, 2012, 12:36 AM
    sinnadurai
    For example for 70mm^2 conductor circumference depends on the construction whether it is flexible,stranded, sector/circular,aluminium or copper conductor etc. For CCC refer manufacturer's cataloque or BS/NEC by quoting type of insulation,method of laying,ambient temperature etc