-   -   200 amp service 4/0 ser cable in 2" conduit? (https://www.askmehelpdesk.com/showthread.php?t=317670)

  • Feb 15, 2009, 03:03 PM
    quick_68
    200 amp service 4/0 ser cable in 2" conduit?
    What should I run from my disconnect switch to my panel box inside for my 200 amp service. I have 2" PVC ran from the disconnect to the panel. I thought about using 4/0 SER but then read somewhere that you are not suppose to put it in conduit because of possible temp problems? Is this correct or faulty information? Also if not SER 4/0 then what should I use?

    Thanks!
  • Feb 15, 2009, 07:19 PM
    Tev

    SER can be used in conduit. In some cases, where subject to physical damage, it is required to be protected by conduit. I would use 2/0 copper or 4/0 aluminum THHN/THWN for your application.