My living room is on a 15 amp breaker. 1 ceiling fan and 11 outlets. Can I pull power from 1 outlet and install 2 3" recessed lights over my bookshelves? Also if this application is acceptable, can I use romex wire to make the connections?
![]() |
My living room is on a 15 amp breaker. 1 ceiling fan and 11 outlets. Can I pull power from 1 outlet and install 2 3" recessed lights over my bookshelves? Also if this application is acceptable, can I use romex wire to make the connections?
Sure, maybe to a switch first?
A word of caution. If the cans are going to be surrounded by insulation make sure you get the correct fixture. Some fixtures require that they not be covered by insulation and others do not have that restriction.
I believe that the breaker will be fine, providing that you have completed a reasonably decent analysis of the load.
Yes, you can move the insulation away from the cans. Make sure the insulation is at least 2" away in all directions from each can.
If your fixture is NON-IC Rated, by reviewing the installation instructions, you will discover that any insulation must be a minimum of THREE inches away, in all directions, thus complying with NEC 2008 Section 410.116 (B).
What difference will a low voltage light make? A watt is a watt and heat is heat.